#91687 - 01/29/05 03:43 PM Do these water lines violate the NEC?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Do these water lines violate the NEC?

_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#91688 - 01/29/05 04:12 PM Re: Do these water lines violate the NEC?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Not directly above panel- I say no.

Working space extends to ceiling. That's not so easy to call. I would consider the "ceiling" to be the bottom flange of the I-joists. Even so, the copper lines attached directly to the flanges I would consider at worst a 'de minimus' (too small to matter) violation.
The drain line is another matter. On balance, I'd let it slide as well. The plumber has little flexibility as to where the drain must run, and there is plenty of room to open the panel. I say this assuming that the vertical part of the drain does not also intrude on working space from the side!
Top
#91689 - 01/29/05 05:33 PM Re: Do these water lines violate the NEC?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
No violation of 110.26(F)(1) at least from the appearance in the elevation shown in the picture.
The question does not ask if the drain line is in violation, only the water lines. We would need another elevation and some dimensions to determine if the drain line violated the working space.
_________________________
George Little
Top
#91690 - 01/29/05 10:46 PM Re: Do these water lines violate the NEC?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
_________________________
Greg Fretwell
Top
#91691 - 01/30/05 12:00 AM Re: Do these water lines violate the NEC?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
I think the plumbing's OK, but the cable work stinks
Top
#91692 - 01/30/05 09:31 AM Re: Do these water lines violate the NEC?
dannynova Offline
Member
Registered: 12/22/03
Posts: 18
Loc: new york
i think there is supposed to be up to a 1/4" inch space between the panel and the concrete wall. thats why we use kindorf or plywood. if true anyone know what nec section this would be.
Top
#91693 - 01/30/05 10:36 AM Re: Do these water lines violate the NEC?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
dannynova- The .25" reference you are looking for is in the NEC at 300.6(C) but I'm hoping it don't apply because if it does, the builder has a problem
The raised mounting holes on the back of the panels are designed to allow air circulation and I don't know how successful they really are. Sometimes the installers use a power pin setter and they don't get the advantage of these .25" standoffs.
_________________________
George Little
Top
#91694 - 01/30/05 01:06 PM Re: Do these water lines violate the NEC?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
I. Installation

312.2 Damp, Wet, or Hazardous (Classified) Locations.

(A) Damp and Wet Locations. In damp or wet locations, surface-type enclosures within the scope of this article shall be placed or equipped so as to prevent moisture or water from entering and accumulating within the cabinet or cutout box, and shall be mounted so there is at least 6 mm (ΒΌ in.) airspace between the enclosure and the wall or other supporting surface. Enclosures installed in wet locations shall be weatherproof.
Exception: Nonmetallic enclosures shall be permitted to be installed without the airspace on a concrete, masonry, tile, or similar surface.

FPN: For protection against corrosion, see 300.6.
_________________________
Joe Tedesco, NEC Consultant
Top
#91695 - 01/30/05 07:25 PM Re: Do these water lines violate the NEC?
HLCbuild Offline
Member
Registered: 12/05/04
Posts: 209
Loc: Herndon,Va USA
Joe,

Are you saying that this installation is in a damp, wet, or classified location...or is this just to clarify the 1/4" space required if it were in one of these locations?
Top
#91696 - 01/30/05 08:28 PM Re: Do these water lines violate the NEC?
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
If the basement of a home is a damp or wet location then the Builder has a problem not the electrician.
_________________________
George Little
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals