The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 07:28 PM
Faricating Guards out if Lexan?
by frank
Today at 04:33 PM
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
Webmaster 10
sparkyinak 9
Who's Online
1 registered (lesk), 193 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#91634 - 01/27/05 08:16 PM Meter Main Bonding
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
We have a 200 amp meter pedistal with a built in 200 amp circuit breaker. About 35' feet away is the first 200 amp panel. An equipment ground is run from the pedistal to the 200 amp panel with the 3 3ott conductors.

The dispute is if the 200 a panel inside should have the main bond screw in (bonding the neutral to ground).

I believe the meter serves as the main disco and is by design bonding the nutral and equipment ground. The inside panel would not be a service panel because the meter is the service. Right?

Then the water pipe ground should go to the meter and not the panel?

Thanks,

Tom

Top
2014 / 2011 NEC & Related Books and Study Guides
#91635 - 01/27/05 09:00 PM Re: Meter Main Bonding
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
If you are running 4 wires you will not reground the neutral at the second panel. That creates a parallel path.
_________________________
Greg Fretwell

Top
#91636 - 01/28/05 03:05 AM Re: Meter Main Bonding
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
I agree, you would not tie the two together in these downstream panels.

Now, whether or not a ground rod is necessary at the down stream panels would be found in 250.32.

Roger

Top
#91637 - 01/28/05 05:07 AM Re: Meter Main Bonding
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
I'd say ground rod or rods at meter base (install bonding screw), 4 wires from meter base to panel at the house. Float neutral bar at the house, Tie water pipe and what every gounding you have to the ground bar at the house.This is simlar to a Trailer hookup . If disconnect was mounted on the house outside then I;d say grounds to to panel outside, when remote I;d say No.

Top
#91638 - 01/28/05 06:44 PM Re: Meter Main Bonding
Steve T Offline
Member

Registered: 02/14/01
Posts: 312
Loc: Oak Park, IL, USA
You have it correct.

Now the next question is--can the GEC pass through the panel? (No splice)

Top
#91639 - 01/29/05 03:04 PM Re: Meter Main Bonding
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
What is the breaker on the pedistal used for ??

Hot sequence or cold??

Just a thought

Charlie

Top
#91640 - 01/30/05 12:31 PM Re: Meter Main Bonding
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
The disconect meter pedistal is mounted on the side of the house. Thanks for yor replys.


Tom

Top
#91641 - 01/30/05 09:03 PM Re: Meter Main Bonding
eswets Offline
Member

Registered: 03/07/04
Posts: 56
Loc: Lansing, IL, USA
Tom,
I had a job like that. 200amp breaker on the meter ped, 200amp mlo panel. 2" ridgid from meter to panel with out bond screw. 3/4" conduit from meter to cold water ground. Thats how inspector wanted it.
BTW were you at leviton's LIN class in Northbrook on thursday? though I saw your company name.

Top
#91642 - 01/30/05 10:21 PM Re: Meter Main Bonding
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
The water piping of the dwelling should be bonded to the EGC buss of the panel at the dwelling. It should not be run separately to the meter main.

Curt
_________________________
Curt Swartz

Top
#91643 - 01/31/05 05:09 AM Re: Meter Main Bonding
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Curt,
If there is metal underground water pipe, then the conductor between the water pipe and the electrical system is a grounding electrode conductor and must be connected to the grounded conductor at or on the line side of the service disconenct per 250.24(A)(1).
Don
_________________________
Don(resqcapt19)

Top