#91634 - 01/28/05 12:16 AM Meter Main Bonding  
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
We have a 200 amp meter pedistal with a built in 200 amp circuit breaker. About 35' feet away is the first 200 amp panel. An equipment ground is run from the pedistal to the 200 amp panel with the 3 3ott conductors.

The dispute is if the 200 a panel inside should have the main bond screw in (bonding the neutral to ground).

I believe the meter serves as the main disco and is by design bonding the nutral and equipment ground. The inside panel would not be a service panel because the meter is the service. Right?

Then the water pipe ground should go to the meter and not the panel?

Thanks,

Tom


2017 / 2014 NEC & Related Books and Study Guides

#91635 - 01/28/05 01:00 AM Re: Meter Main Bonding  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,057
Estero,Fl,usa
If you are running 4 wires you will not reground the neutral at the second panel. That creates a parallel path.


Greg Fretwell

#91636 - 01/28/05 07:05 AM Re: Meter Main Bonding  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
I agree, you would not tie the two together in these downstream panels.

Now, whether or not a ground rod is necessary at the down stream panels would be found in 250.32. [Linked Image]

Roger


#91637 - 01/28/05 09:07 AM Re: Meter Main Bonding  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
I'd say ground rod or rods at meter base (install bonding screw), 4 wires from meter base to panel at the house. Float neutral bar at the house, Tie water pipe and what every gounding you have to the ground bar at the house.This is simlar to a Trailer hookup . If disconnect was mounted on the house outside then I;d say grounds to to panel outside, when remote I;d say No.


#91638 - 01/28/05 10:44 PM Re: Meter Main Bonding  
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
You have it correct.

Now the next question is--can the GEC pass through the panel? (No splice)


#91639 - 01/29/05 07:04 PM Re: Meter Main Bonding  
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
What is the breaker on the pedistal used for ??

Hot sequence or cold??

Just a thought

Charlie


#91640 - 01/30/05 04:31 PM Re: Meter Main Bonding  
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
The disconect meter pedistal is mounted on the side of the house. Thanks for yor replys.


Tom


#91641 - 01/31/05 01:03 AM Re: Meter Main Bonding  
eswets  Offline
Member
Joined: Mar 2004
Posts: 55
Lansing, IL, USA
Tom,
I had a job like that. 200amp breaker on the meter ped, 200amp mlo panel. 2" ridgid from meter to panel with out bond screw. 3/4" conduit from meter to cold water ground. Thats how inspector wanted it.
BTW were you at leviton's LIN class in Northbrook on thursday? though I saw your company name.


#91642 - 01/31/05 02:21 AM Re: Meter Main Bonding  
caselec  Offline
Member
Joined: Apr 2002
Posts: 558
San Jose, CA
The water piping of the dwelling should be bonded to the EGC buss of the panel at the dwelling. It should not be run separately to the meter main.

Curt


Curt Swartz

#91643 - 01/31/05 09:09 AM Re: Meter Main Bonding  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Curt,
If there is metal underground water pipe, then the conductor between the water pipe and the electrical system is a grounding electrode conductor and must be connected to the grounded conductor at or on the line side of the service disconenct per 250.24(A)(1).
Don


Don(resqcapt19)

Page 1 of 2 1 2

Member Spotlight
mersadrad
mersadrad
Montreal, Quebec, Canada
Posts: 28
Joined: March 2011
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.024s Queries: 15 (0.004s) Memory: 0.8149 MB (Peak: 0.9897 MB) Zlib enabled. Server Time: 2017-03-25 19:41:20 UTC