The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 164 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91631 - 01/27/05 04:49 PM shunt trip breaker
dabest Offline
Junior Member

Registered: 01/26/05
Posts: 5
fello electricians i was wandering if someone could answer a ? in a commercial kitchen when the shunt trip kills power to asub panel how should i keep the exhaust opperational ? mov it to another panel not controled by shunt ? excuse the typing snafus and thanks

Top
2017 / 2014 NEC & Related Books and Study Guides
#91632 - 01/28/05 11:26 AM Re: shunt trip breaker
Geno Offline
Member

Registered: 08/27/01
Posts: 16
Loc: Syracuse, NY USA
Yes, thats what we do, in fact we also add a contactor to turn the exhaust fan on if the fire protection system should activate to allow any smoke and fumes to be exhausted.

Top
#91633 - 01/28/05 11:35 AM Re: shunt trip breaker
dabest Offline
Junior Member

Registered: 01/26/05
Posts: 5
thanks geno i like the contactor idea i appreciate it