The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (gfretwell), 129 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91618 - 01/25/05 08:14 AM High Leg Practice
Ragu Offline
Junior Member

Registered: 06/01/01
Posts: 7
Loc: Elkton, Md USA
I have a delta-delta xmfr feeding a 240V panel. 2 phases to X4 (neutral) provide 120V, the 3rd phase, or Hi leg will not produce 120V to X4.

My question is around acceptable practice. Can the neutral (X4) be run to the panel and the 3rd phase marked as "Hi Leg do not use for 120V single phase". I've seen this done but I'm wondering
1-Is this a code violation?
2-Is this "good" practice? Or should 120V just not be fed from this panel. Don't run the neutral (X4) to the panel and therefore no mistake can be made?

Thanks

Top
2014 / 2011 NEC & Related Books and Study Guides
#91619 - 01/25/05 09:36 AM Re: High Leg Practice
gfretwell Online   content

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
110.15 High-Leg Marking.
On a 4-wire, delta-connected system where the midpoint of one phase winding is grounded to supply lighting and similar loads, the conductor or busbar having the higher phase voltage to ground shall be durably and permanently marked by an outer finish that is orange in color or by other effective means. Such identification shall be placed at each point on the system where a connection is made if the grounded conductor is also present.
_________________________
Greg Fretwell

Top
#91620 - 01/25/05 09:57 AM Re: High Leg Practice
Anonymous
Unregistered


See also 408.3 (E) High leg on B phase.
See 250.24 (B) Grounded conductor required to be brought to service equipment.
See 250.20 (B) System required to be grounded.

Top
#91621 - 01/25/05 03:59 PM Re: High Leg Practice
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
 
Buried on the IEEE C57.12 transformer standards are two variations for tapped-delta secondary terminal designations. If the highleg is across from grounded terminal X2, it is labeled X6. If the highleg is across from grounded terminal X3, it is labeled X4.



If 120V is needed {say for controls} it would be grounded to form a separately derived system, although not a “:neutral” for the unsymmetrical phase-to-ground voltages. If the corresponding delta-tap terminal is grounded, highleg marking is in order for your and others’ safety.

Top
#91622 - 01/25/05 07:34 PM Re: High Leg Practice
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
All marking requirements aside, from a design stand point the most fool proof way is to not bring the high leg phase to your 120V panels. Feed three phase loads from separate 3 phase panels with no neutral taken to them. Feed 120V panels single phase + N. No high leg. I did a church once that was designed this way and it worked out well.