The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 285 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91615 - 01/25/05 05:17 AM Outside Of Building?
GamecockEE Offline

Registered: 07/28/04
Posts: 49
Loc: Georgetown, SC 29440
I recently did a design for five town homes that are individually owned but share a common floor slab and are separated by firewalls. I utilized gangable meterbases with the main disconnects for each town homes(being circuit breakers)located on the outside of the building. The main feeder for each town home then travels underground below the slab in RNC sched 40 to each town home power panel.

My question is are these feeder conduits considered to be outside the building. Does article 230.6 cover this situation, or is there another section of code that is applicable to this. I realize that these are not service conductors since they are downstream of the first disconnecting means.

2014 / 2011 NEC & Related Books and Study Guides
#91616 - 01/25/05 09:31 AM Re: Outside Of Building?
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
225.10, 225.22, 300.5, 310.15(B)6) ...
What is the questionable part?
Greg Fretwell

#91617 - 01/25/05 09:44 AM Re: Outside Of Building?
hbiss Offline

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Per 230.6(1) they are outside the building no?

That aside, they are not service conductors so they do not have to be outside the building.