The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91584 - 01/24/05 10:45 AM UL vs. NEC
martinvalley Offline
Junior Member

Registered: 01/21/05
Posts: 1
Loc: Westwood, NJ, USA
Trying to get ahnadle on NEC rating or use vs. UL approval. For instance, if a cstrain relife cord grip fittings is UL listed to Standard 514B, would this amke it suitable for use in a Class I, Division II, Group D environment. Is there a relationship or crossover between UL and NEC?

Top
2014 / 2011 NEC & Related Books and Study Guides
#91585 - 01/24/05 12:37 PM Re: UL vs. NEC
safetygem Offline
Member

Registered: 01/30/02
Posts: 114
Loc: Ohio, USA
I do not believe there are any restrictions on the use of strain relief devices in Classified Locations. I say this because... the NEC allows the use of "general-purpose" equipment in Division 2 locations when:
 Quote:
500.8(A)(3) Where specifically permitted in Articles 501 through 503, general-purpose equipment or equipment in general-purpose enclosures shall be permitted to be installed in Division 2 locations if the equipment does not constitute a source of ignition under normal operating conditions.


BTW, scope of UL 514b covers a wide variety of equipment. Some of the equipment has been tested for use in classified locations... but not all of it has been tested for this use.

Hope this helps.

Top
#91586 - 01/24/05 07:17 PM Re: UL vs. NEC
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
There is absolutely NO connection between any NEC section number, and the number of a UL standard.

UL does test electrical equipment, and the NEC plays an important part in determining what the test criteria may be....but UL test to a lot of standards that have nothing to do with the electrical trade.

The best source as to what a particuler UL standard, or listing, means is the UL web site.

The best place to discuss the code is, frankly, this web site. How and why the NFPA let this happen is a secret know only to them!

Top
#91587 - 01/25/05 02:05 PM Re: UL vs. NEC
safetygem Offline
Member

Registered: 01/30/02
Posts: 114
Loc: Ohio, USA
John... you are absolutely right. I should have made your point about correlation clear in my post.

BTW... for any that are interested. You can always look at the scope of a UL standard and determine fundamentally what the intended usage is for a piece of equipment.

All UL standard scopes can be reviewed on their website at the following address: http://ulstandardsinfonet.ul.com/scopes/

[This message has been edited by safetygem (edited 01-25-2005).]