The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91579 - 01/23/05 08:01 PM An EC worked this up. Does this seem correct?
Load-n-Code Offline
Member

Registered: 01/08/05
Posts: 20
Loc: CA, USA
An EC worked this up. Does this seem correct...

Computed Load;
Noncontinuous Loads
Receptical Load;
42 duplex recepticals @ 180 volt-ampere 7560
7560 volt-amperes @ 100% 7560
Total Noncontinuous Load: 7560
Continuous Loads;
General Lighting Load;
--1482 sq. ft. at 3 volt-amperes per sq. ft 4446
Show Window Lighting Load;
--12ft at 200 volt-amperes per ft. 2400

Outside Sign Circuit 1200 volt-amperes 1200
Total Continuous Load: 8046

Total Non-Continuous Load plus Continuous Load: 15606

Minimum Size Feeder Overcurrent Protection
--Total noncontinuous loads 7560
--Total continuous loads @ 125% (8046*1.25) 10058
Total Load: 17618

17618 volt-amperes / 208 volts = 85 amperes
The next higher standard is 100 amperes

Minimum Size Feeders
-- 15606 volt-amperes / 208 volts = 75 amperes

Feeder size #2 cu THHN or #1 TW

---------------------
What is actually at the space
---------------------
The retail space is 1482 s.f. & has ...
---
42 duplex receptacles
(27 of them located on 9 separate ckts. 3 duplex recepts / ckt. at ea. salon stylist station)
---
2 duplex recepts. ceiling mounted at storefront.
---
2 conv. duplex recepts at front desk in addition to
1 dedicated for the cash register/computer
---
2 conv. duplex recepts. in the retail area
---
3 duplex recepts. for sit down hair dryers
---
5 conv. recepts. in the stock room
---

There is also...
1 - 18kW water heater
1 - 8A Automatic Washer
1 - 12A Automatic Dryer
2 - Exit/Emergency Light
1 - Exit Light
1 - Emergency Light
1 - 2-1/2 ton AC - 208y/120 1phase 23.3A 40OCP
1 - J-Box for exterior sign

Lighting
12 - 4 lamp 2'x4' recessed fluorescent fixtures (can lamp with 32w lamps)
1 - 2 u-lamp 2'x2'
1 - fan restroom
2 - 2 lamp 8' fluorescent strip light
4 - recessed incandescent can type fixtures

-----------------
Please help educate me...

Thanks,
--Mario


[This message has been edited by Load-n-Code (edited 01-25-2005).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#91580 - 01/23/05 08:42 PM Re: An EC worked this up. Does this seem correct?
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
Why did you not include this load in the calcuations? It the service 120/208 3 phase?

1 - 18kW water heater
1 - 8A Automatic Washer
1 - 12A Automatic Dryer
2 - Exit/Emergency Light
1 - Exit Light
1 - Emergency Light
1 - 2-1/2 ton AC - 208y/120 1phase 21A 40OCP



[This message has been edited by Bob (edited 01-23-2005).]

Top
#91581 - 01/23/05 10:36 PM Re: An EC worked this up. Does this seem correct?
Load-n-Code Offline
Member

Registered: 01/08/05
Posts: 20
Loc: CA, USA
NEC 2002
220.13 Demand Factors for Non-Dwelling Receptacle Loads
Which receptacles are included in the total?
(just the 42 receptacles @ 7560VA, correct?)

That was the question...
These were left out should I calculate these as follows...

NLCL - Non-Continuous Load
LCL - Continuous Load

1 - 18kW water heater
NLCL - 18248VA

1 - 8A Automatic Washer
NLCL - 960VA

1 - 12A Automatic Dryer
NLCL - 1440VA

2 - Exit/Emergency Light
LCL - 225VA

1 - Exit Light
LCL - 63VA

1 - Emergency Light
LCL - 94VA

1 - 2-1/2 ton AC - 208y/120 1phase 23.3A 40OCP
23.3A * 208V = 4646.4VA

Thanks,
--Mario

[This message has been edited by Load-n-Code (edited 01-25-2005).]

Top
#91582 - 01/25/05 02:54 PM Re: An EC worked this up. Does this seem correct?
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
I would consider the WH, Dryer and AC and continuous loads.

Top
#91583 - 01/26/05 02:04 AM Re: An EC worked this up. Does this seem correct?
Load-n-Code Offline
Member

Registered: 01/08/05
Posts: 20
Loc: CA, USA
Bob,
Thanks

--Mario

Top