#91519 - 01/20/05 04:23 PM main breaker
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
where does it say that the main breaker has to be at the meter if the panel is so far away? i can't seem to find this.
Top
2017 / 2014 NEC & Related Books and Study Guides
#91520 - 01/20/05 04:29 PM Re: main breaker
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sid, the closest you'll get is 230.70(A)(1).

This pretty much leaves it up to the AHJ and local requirements.

Roger
Top
#91521 - 01/20/05 05:13 PM Re: main breaker
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
maybe its local code...
Top
#91522 - 01/20/05 05:17 PM Re: main breaker
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
they say (some people) if its back to back you can put your main in the panel....
Top
#91523 - 01/20/05 05:31 PM Re: main breaker
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sid, have you read 230.70(A)(1)?

Roger
Top
#91524 - 01/20/05 05:35 PM Re: main breaker
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
yes, its not very specific. nearest point.... then 30 or 50 feet from the meter would be fine.. right? or is nearest point always the meter? those meter mains are 100 buck plus the mlo is 100 too. just trying to save a 100
Top
#91525 - 01/20/05 05:58 PM Re: main breaker
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sid,
Quote:
they say (some people) if its back to back you can put your main in the panel....
they are right, this meets the requirement of 230.70(A)(1).

This can be as much as 5,6, or even 10' in some locations. I don't know of any where that would allow 50', however you might want to look at 230.6 if you must run this far.

Roger
Top
#91526 - 01/20/05 06:00 PM Re: main breaker
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
thanks roger
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals