#91378 - 01/13/05 10:17 AM riser
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 49
Loc: warren mi us
IS IT acsecptable for the power company service line to run over liveable dwelling?If it is how far off the roof does it need to be?
Top
2017 / 2014 NEC & Related Books and Study Guides
#91379 - 01/13/05 10:23 AM Re: riser
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Yes, 230.24(A)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#91380 - 01/28/05 10:58 AM Re: riser
dabest Offline
Junior Member
Registered: 01/26/05
Posts: 5
it is acceptable so long as the point of attachment sustains a 3' clearance above roof for the roofers sake
Top
#91381 - 01/28/05 11:52 AM Re: riser
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
That 3' is only "final conductor span" leading to the service head. Normally the clearance is 8' above the roof for a distance of 3' beyond the roof edge.
_________________________
Greg Fretwell
Top
#91382 - 01/29/05 10:02 AM Re: riser
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
Actually, the NESC is the Code that covers the serving electric utility’s service drop clearances. The 3 ft beyond the roof’s edge is not in the NESC.

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#91383 - 01/29/05 06:24 PM Re: riser
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
What is the NESC rule for height over a roof?
_________________________
Greg Fretwell
Top
#91384 - 01/29/05 07:19 PM Re: riser
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
It's up to the POCO. Here they won't allow the eight foot riser if it's more than 3 feet from the edge because they don't allow the line crews to use a ladder on the roof for safety reasons. So they specify five feet, no matter how much of the drop extends over the roof.
Top
#91385 - 01/30/05 06:23 PM Re: riser
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
These are "before and after" photos of one result of a service change I did. As you can see, the service drop has a lot more clearance than it previously had.

So, yes, you can run these conductors over a dwelling, but you do need 36" clearance. While I believe that this is covered in NEC 230-24, your local utility is likely to have a different rule.

- renosteinke
Top
#91386 - 01/30/05 06:39 PM Re: riser
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
If this drop is not going to the building in question I think 230.24 says it has to be 8 feet above the roof, out to a distance of 3 feet from the roof's edge. The exception (4) is for the final span of the drop that connects to the riser on the building served
_________________________
Greg Fretwell
Top
#91387 - 02/01/05 05:37 PM Re: riser
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Somehow the "before" and "after shots got reversed . I hate it when that happens!
I will admit that 230 also references the pitch of the roof; this roof is right on the line, and I let the inspector decide. Part of this was based upon the heigth of the riser on the building getting new service; see photos added to "flagpoles" in "photos submitted for discussion."
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals