The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91375 - 01/13/05 05:31 AM Required Outlet For Mop Sink | Counters
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Is there a requirement to have an outlet at a mop sink in a basement of a house?

Is there a requirement for having outlets along counters that are not in a kitchen but a rec room or other area of a house?

Thanks for any replies.

-regards

Mustang
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#91376 - 01/13/05 05:29 PM Re: Required Outlet For Mop Sink | Counters
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Mustang:
No; but if it is an "unfinished" basement there MUST be 1-GFI recept.

A counter in a rec room poses an interesting point. Not knowing the layout or dimensions of the room & counter doesn't help. The basic 6-12 spacing, and >24" have to be complied with; if the 'counter' fits between the required wall recept, then I will say "NO, you do not need any more by code.

Remember, the NEC is not a design manual, only the minimum requirements for your question.

John
_________________________
John

Top
#91377 - 01/13/05 05:40 PM Re: Required Outlet For Mop Sink | Counters
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Thanks for the reply...this is a minimum install by design..

only what is required..

there is a 2 foot by four foot counter top for a microwave and whatever else.

i was not for sure if an outlet was required at any counter or not.

this is is finished basement.

I put one dedicated for the mic and one in the center of the 4 foot section.

i can add another if needed.

thanks for the reply

-regards

greg
_________________________
Electricity has no respect for ignorance!