#91353 - 01/11/05 05:11 PM Bathroom Lights
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
I wired a bathrooms lighting circuit on a GFCI protected circuit.I also have a seperate 20 amp GFCI circuit for the plugs next to the sink.

Well the inspector doesn't want all the lighting on a GFCI circuit. He wants one light in the bath wired to another circuit seperate from the GFCI circuit that all the other lights are on.

Is there anything in the code requiring us to wire bathroom lighting like this? Maybe he is thinking of a old rule from a previous code...I can't find any rule in the 2002 NEC.

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#91354 - 01/11/05 05:53 PM Re: Bathroom Lights
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
No such requirement
_________________________
Greg Fretwell
Top
#91355 - 01/11/05 08:18 PM Re: Bathroom Lights
Physis Offline
Member
Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
I like to say that the inspector is welcome to run the idea pass the owner and or GC and if his proposal is accepted some one can give him an estimate for the cost of the changes he would like.
_________________________
Sam, San Francisco Bay Area
Top
#91356 - 01/11/05 09:37 PM Re: Bathroom Lights
cpal Offline
Member
Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
There was a previous requirement in the Mass Code 1996 (210-70 d) that restricted all the lighting in an area from depending on a GFCI. The issue considered leaving the area in total darkness during the event of a failure of the GFCI. This requirement was deleted in 1999. The Committee recognized that nuisance tripping of these devices is less likely than previously encountered.
Top
#91357 - 01/11/05 09:40 PM Re: Bathroom Lights
kd Offline
Member
Registered: 12/14/04
Posts: 51
Years ago, there was a requirement that every bedroom have outlets fed from two different circuits, but that is gone with the wind. Every violation should have a reference to the Code. Also the inspector is not the boss, the head of the building department is the boss.
Top
#91358 - 01/12/05 01:32 AM Re: Bathroom Lights
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
cpal...thankyou for looking up the old code reference.I remember having to wire bath lights seperate from the load side of the bath GFCI plug so the lights wouldn't go out when the GFCI tripped.This was before 20 amp circuits were required for the bath plugs.

shortcircuit
Top
#91359 - 01/12/05 07:36 AM Re: Bathroom Lights
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
From the 2005 Mass Electrical code " 210.70 (D) GFCI Protection of lighting outlets in all ocupancies. The operation of a single GFCI device shall not deenergize all lighting outlets in a given area." If the job is permitted after 1/01/05 Inspector is correct. If not you are ok. Why is the lighting circuit gfci protected anyway?
Top
#91360 - 01/12/05 09:34 AM Re: Bathroom Lights
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
I have a exhaust fan/light over a shower that needs GFCI protection according to the instructions with the unit. I also have recessed lights over the cuzi tub which I like to have GFCI protected.

So I feed the 3-gang switch box for the lights in the bathroom with the load side of a GFCI plug located near the bathroom...in the master closet for the master bathroom.I'll locate a GFCI plug outside the bathroom in the upper hallway for the main bath.This way it is nearby for the homeowner to reset.

shortcircuit
Top
#91361 - 01/12/05 11:36 AM Re: Bathroom Lights
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
I usually just use the receptacle gfci circuit to feed the fan if it is over a shower.
Top
#91362 - 01/12/05 04:35 PM Re: Bathroom Lights
Norstarr Offline
Member
Registered: 09/25/04
Posts: 89
Loc: Wi
The code only requires the receptacle to be gfi protected. The code also states that if the separate 20 amp circuit to the bathroom is dedicated you can use it for the lighting and exhaust fans also for that one bathroom. Put the lighting on the line side of the gfi receptacle. Is his requirement for a second circuit for the lighting a local ordinance or his own preferance. If it isn't a local ordinance I would protest that he was missing when you quoted the job.
Ron
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM
Looking for older post
by Texas_Ranger
01/21/17 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM

The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades