The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 119 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91303 - 01/09/05 07:00 AM torque
kd Offline

Registered: 12/14/04
Posts: 51
When I torque lugs using Aluminum wire, I will apply, say 50 ft. lbs., then several days later check the torque. It will be down to, say, 35 lbs, so I re-torque it. Other ECs say you should just torque it and forget it--that the loss in tightness is built-in to the required torque. Of course Copper holds its torque so it is not a problem. What do you guys and gals say about this?

2014 / 2011 NEC & Related Books and Study Guides
#91304 - 01/09/05 07:47 AM Re: torque
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Torque it once to the specifications for the lug & leave it alone.
Few things are harder to put up with than the annoyance of a good example.

#91305 - 01/09/05 08:37 AM Re: torque
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
How does an inspector know how much you've torqued a connection? I am a fan of the break away connection.
George Little

#91306 - 01/09/05 09:38 PM Re: torque
Physis Offline

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
Another reason to not like aluminum as a conductor.
Sam, San Francisco Bay Area

#91307 - 01/10/05 04:13 PM Re: torque
John Steinke Offline

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
Not "another" reason- THE reason! Aluminum is notorious for "creep" when over-torqued. Aluminum should not be torqued to the same values as copper for this reason.
Simply put, too much pressure causes the metal to flow, leaving you with a loose connection. Make sure the value you're using is the correct on, and not "something always used."

#91308 - 01/11/05 09:31 PM Re: torque
kd Offline

Registered: 12/14/04
Posts: 51
Aluminum association torque table shows the sasme values for Cooper and Aluminum.

#91309 - 01/17/05 05:24 PM Re: torque
Nick Offline

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA

#91310 - 01/18/05 08:21 AM Re: torque
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
The following is a very important quote from the document that Nick has posted a link to.
It is often asked whether bolted connections require periodic retightening. The simple answer is NO. Once the connector is installed with the proper torque, repeated tightening could actually damage the connector and/or the conductor and eventually lead to a failure.