The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91303 - 01/09/05 07:00 AM torque
kd Offline
Member

Registered: 12/14/04
Posts: 51
When I torque lugs using Aluminum wire, I will apply, say 50 ft. lbs., then several days later check the torque. It will be down to, say, 35 lbs, so I re-torque it. Other ECs say you should just torque it and forget it--that the loss in tightness is built-in to the required torque. Of course Copper holds its torque so it is not a problem. What do you guys and gals say about this?

Top
2014 / 2011 NEC & Related Books and Study Guides
#91304 - 01/09/05 07:47 AM Re: torque
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Torque it once to the specifications for the lug & leave it alone.
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#91305 - 01/09/05 08:37 AM Re: torque
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
How does an inspector know how much you've torqued a connection? I am a fan of the break away connection.
_________________________
George Little

Top
#91306 - 01/09/05 09:38 PM Re: torque
Physis Offline
Member

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
Another reason to not like aluminum as a conductor.
_________________________
Sam, San Francisco Bay Area

Top
#91307 - 01/10/05 04:13 PM Re: torque
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
Not "another" reason- THE reason! Aluminum is notorious for "creep" when over-torqued. Aluminum should not be torqued to the same values as copper for this reason.
Simply put, too much pressure causes the metal to flow, leaving you with a loose connection. Make sure the value you're using is the correct on, and not "something always used."

Top
#91308 - 01/11/05 09:31 PM Re: torque
kd Offline
Member

Registered: 12/14/04
Posts: 51
Aluminum association torque table shows the sasme values for Cooper and Aluminum.

Top
#91309 - 01/17/05 05:24 PM Re: torque
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA

Top
#91310 - 01/18/05 08:21 AM Re: torque
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The following is a very important quote from the document that Nick has posted a link to.
 Quote:
It is often asked whether bolted connections require periodic retightening. The simple answer is NO. Once the connector is installed with the proper torque, repeated tightening could actually damage the connector and/or the conductor and eventually lead to a failure.

Don
_________________________
Don(resqcapt19)

Top