#91238 - 01/06/05 03:21 AM Hot Tub Disconnect
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?

The 50 amp GFCI breaker isn't within sight of the tub.

shortcircuit
Top
2017 / 2014 NEC & Related Books and Study Guides
#91239 - 01/06/05 04:29 AM Re: Hot Tub Disconnect
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Yes disco is needed. 680.12
Top
#91240 - 01/06/05 05:41 AM Re: Hot Tub Disconnect
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)

shortcircuit
Top
#91241 - 01/06/05 07:19 PM Re: Hot Tub Disconnect
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
The emergency disconnect is not required at single family dwellings.
Top
#91242 - 01/06/05 07:38 PM Re: Hot Tub Disconnect
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.
Top
#91243 - 01/10/05 06:46 PM Re: Hot Tub Disconnect
harold endean Offline
Member
Registered: 02/16/02
Posts: 2233
Loc: Boonton, NJ
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?
Top
#91244 - 01/10/05 08:16 PM Re: Hot Tub Disconnect
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99
_________________________
George Little
Top
#91245 - 01/11/05 02:52 AM Re: Hot Tub Disconnect
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?

shortcircuit
Top
#91246 - 01/11/05 04:09 PM Re: Hot Tub Disconnect
mike d Offline
Junior Member
Registered: 01/04/05
Posts: 9
Loc: new jersey
680.12 says the disconnecting means shall be
accessible & within sight from its equipment

look at the definition of accessible, I do
not think the disconnect under the spa meets
that requirement.
Top
#91247 - 01/11/05 08:19 PM Re: Hot Tub Disconnect
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.
_________________________
George Little
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals