ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
Old decora style outlets
by switches. 03/25/17 10:31 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,429 Are you busy
166,147 Re: Forum
160,604 Need opinion
Who's Online Now
1 registered members (Admin), 79 guests, and 15 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
Page 1 of 2 1 2
#91238 - 01/06/05 07:21 AM Hot Tub Disconnect  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?

The 50 amp GFCI breaker isn't within sight of the tub.

shortcircuit


2017 / 2014 NEC & Related Books and Study Guides

#91239 - 01/06/05 08:29 AM Re: Hot Tub Disconnect  
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Yes disco is needed. 680.12


#91240 - 01/06/05 09:41 AM Re: Hot Tub Disconnect  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)

shortcircuit


#91241 - 01/06/05 11:19 PM Re: Hot Tub Disconnect  
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
The emergency disconnect is not required at single family dwellings.


#91242 - 01/06/05 11:38 PM Re: Hot Tub Disconnect  
BigB  Offline
Member
Joined: Mar 2004
Posts: 719
Tucson, AZ USA
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.


#91243 - 01/10/05 10:46 PM Re: Hot Tub Disconnect  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?


#91244 - 01/11/05 12:16 AM Re: Hot Tub Disconnect  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99


George Little

#91245 - 01/11/05 06:52 AM Re: Hot Tub Disconnect  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?

shortcircuit


#91246 - 01/11/05 08:09 PM Re: Hot Tub Disconnect  
mike d  Offline
Junior Member
Joined: Jan 2005
Posts: 9
new jersey
680.12 says the disconnecting means shall be
accessible & within sight from its equipment

look at the definition of accessible, I do
not think the disconnect under the spa meets
that requirement.


#91247 - 01/12/05 12:19 AM Re: Hot Tub Disconnect  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.


George Little

Page 1 of 2 1 2

Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.019s Queries: 15 (0.003s) Memory: 0.8136 MB (Peak: 0.9877 MB) Zlib enabled. Server Time: 2017-03-25 15:43:01 UTC