I need some help with this one. If you have a closet that is 24" deep can you install a light in there? I've read the codes and it gets a little confusing. If you use a dome covered pullchain, you have to be 12" from the egde of the self (the selfs are usually 12") and 6" from the other wall. You will need a 36" Closet to do this. A can light can be 6" from edge so with that you need a 30" closet. Am I just messing this all up or am I right, b/c all of the prints I get have 24" closets with lights in them.
Top
2017 / 2014 NEC & Related Books and Study Guides
#91228 - 01/05/05 09:32 PM Re: Closet lights
Physis Offline
Member
Registered: 12/28/04
Posts: 86
Loc: Burlingame, Ca. USA
If your closet is only 24" deep you will need to use recessed.

And the edge of the recessed fixture toward the rear has to be 18" from the rear wall.

And the shelf if any must be 6" from the edge of the fixture.

That doesn't address the 6' or hight of hanger rod off the floor.
_________________________
Sam, San Francisco Bay Area
Top
#91229 - 01/05/05 09:46 PM Re: Closet lights
Norstarr Offline
Member
Registered: 09/25/04
Posts: 86
Loc: Wi
Install a covered fluorescant fixture over the door and your covered. Very nice light and if you want a pull chain it will be right by the door. If you have Menards by you they have a fluorescant just for that with a pull chain.
Ron
Top
#91230 - 01/05/05 11:49 PM Re: Closet lights
Physis Offline
Member
Registered: 12/28/04
Posts: 86
Loc: Burlingame, Ca. USA
410.8(D)(2)seems to allow it. I think you're right Ron.

My Charles Miller disagrees but who's he?
_________________________
Sam, San Francisco Bay Area
Top
#91231 - 01/06/05 05:52 AM Re: Closet lights
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
The fluorescent doesn't have to be covered if it's 6" from the storage space but I would recommend that it is, 410.8(D)(2).
_________________________
George Little
Top
#91232 - 01/06/05 02:48 PM Re: Closet lights
GTE Offline
Member
Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
George,
Flourescents have to be 6" from from the storage area whether it is covered or not.
Top
#91233 - 01/06/05 03:03 PM Re: Closet lights
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
GTE- I agree and my wording was poor so I appreciate the clarification. Could also be noted that the storage space below the shelf is often times larger than above the shelf and the clearances apply here too.
_________________________
George Little
Top
#91234 - 01/06/05 03:48 PM Re: Closet lights
mike d Offline
Junior Member
Registered: 01/04/05
Posts: 9
Loc: new jersey
how wide is the closet? keep in mind 410.8 says storage space is the sides & back wall,
a 12" shelf is figured on sides & back wall
even if no shelfs are installed, you must also take the side walls into consideration
also.
Top
#91235 - 01/06/05 04:47 PM Re: Closet lights
eswets Offline
Member
Registered: 03/07/04
Posts: 55
Loc: Lansing, IL, USA
So if there is no self in the closet, can the light be in the middle of a 24" closet? Or do you have to assume that one day someone can put in a self.
Top
#91236 - 01/07/05 05:24 PM Re: Closet lights
Physis Offline
Member
Registered: 12/28/04
Posts: 86
Loc: Burlingame, Ca. USA
I just decided that this section is so terribly writen that I could solve the Rubix cube before sorting this mess out.

Good luck.
_________________________
Sam, San Francisco Bay Area
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals