#91203 - 01/04/05 05:39 PM Snow Melting Equipment
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Need some information on electric snow melting equipment as used in sidewalks and driveways. Are there any type that don't require GFPE? Web sites would be useful.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#91204 - 01/04/05 07:01 PM Re: Snow Melting Equipment
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
George,
The only electric sidewalk snow melting equipment that does require GFP is that made from MI cable.
Here is one source.
Don
_________________________
Don(resqcapt19)
Top
#91205 - 01/04/05 08:26 PM Re: Snow Melting Equipment
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Don - I think you've miss read the reference for GFPE protection. The site makes reference to their product as MI cable with a "plastic" type covering. NEC '02 says that MI cable does not need GFPE protection. 426.28. Please double check for me.
_________________________
George Little
Top
#91206 - 01/05/05 08:20 AM Re: Snow Melting Equipment
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
George,
My post is wrong. It should read.
"The only electric sidewalk snow melting equipment that does require not GFP is that made from MI cable.
Sorry.


[This message has been edited by resqcapt19 (edited 01-05-2005).]
_________________________
Don(resqcapt19)
Top
#91207 - 01/05/05 03:08 PM Re: Snow Melting Equipment
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Don- You are forgiven.
_________________________
George Little
Top
#91208 - 01/06/05 09:10 AM Re: Snow Melting Equipment
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
Here's a link to one that does not require GFP:
http://www2.northerntool.com/product-1/266859.htm

Tom
Top
#91209 - 01/06/05 02:58 PM Re: Snow Melting Equipment
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Tom (Active 1) That's what I like a guy with a sense of humor. And this inspector agrees with you- No GFP required for this snow melting equipment
_________________________
George Little
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals