The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91203 - 01/04/05 05:39 PM Snow Melting Equipment
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Need some information on electric snow melting equipment as used in sidewalks and driveways. Are there any type that don't require GFPE? Web sites would be useful.
_________________________
George Little

Top
2017 / 2014 NEC & Related Books and Study Guides
#91204 - 01/04/05 07:01 PM Re: Snow Melting Equipment
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
George,
The only electric sidewalk snow melting equipment that does require GFP is that made from MI cable.
Here is one source.
Don
_________________________
Don(resqcapt19)

Top
#91205 - 01/04/05 08:26 PM Re: Snow Melting Equipment
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don - I think you've miss read the reference for GFPE protection. The site makes reference to their product as MI cable with a "plastic" type covering. NEC '02 says that MI cable does not need GFPE protection. 426.28. Please double check for me.
_________________________
George Little

Top
#91206 - 01/05/05 08:20 AM Re: Snow Melting Equipment
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
George,
My post is wrong. It should read.
"The only electric sidewalk snow melting equipment that does require not GFP is that made from MI cable.
Sorry.


[This message has been edited by resqcapt19 (edited 01-05-2005).]
_________________________
Don(resqcapt19)

Top
#91207 - 01/05/05 03:08 PM Re: Snow Melting Equipment
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Don- You are forgiven.
_________________________
George Little

Top
#91208 - 01/06/05 09:10 AM Re: Snow Melting Equipment
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
Here's a link to one that does not require GFP:
http://www2.northerntool.com/product-1/266859.htm

Tom

Top
#91209 - 01/06/05 02:58 PM Re: Snow Melting Equipment
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Tom (Active 1) That's what I like a guy with a sense of humor. And this inspector agrees with you- No GFP required for this snow melting equipment
_________________________
George Little

Top