The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91199 - 01/04/05 09:46 AM Sub panel
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
While visiting another furum I read a disscusion on sub panels.They must have 4 wires back to the main panel.They also stated in the main panel the neutral and grounds must be separated and not bonded together at main panel.If you have only 3 wire service at the main panel the grounds and neutrals would have to tie or the ground fault path wouldn`t trip the breaker. Did I totally miss something.was it a type o.

Top
2014 / 2011 NEC & Related Books and Study Guides
#91200 - 01/04/05 10:01 AM Re: Sub panel
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
I believe that either it was misstated in the discussion or you misread it but in the service equipment the EGC's and the service equipment enclosure are bonded to the grounded service conductor (i.e. the neutral). This provides the fault clearing path.
_________________________
John

Top
#91201 - 01/04/05 03:51 PM Re: Sub panel
Physis Offline
Member

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
Do you mean:

[1] neutral
[2] (red) leg
[3] (black) leg
[4] Grounding conductor

The service does not provide a grounding conductor. That's why the service has only three conductors. The GEC at the service is where the grounding conductor comes from and it can only be connected to the service neutral at one point and that is at the service.
_________________________
Sam, San Francisco Bay Area

Top
#91202 - 01/04/05 03:53 PM Re: Sub panel
Physis Offline
Member

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
After reading your post again. Did they leave out the main bonding jumper?