The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 04:10 PM
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
ghost307 6
renosteinke 6
Potseal 4
Who's Online
1 registered (HotLine1), 162 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91199 - 01/04/05 09:46 AM Sub panel
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
While visiting another furum I read a disscusion on sub panels.They must have 4 wires back to the main panel.They also stated in the main panel the neutral and grounds must be separated and not bonded together at main panel.If you have only 3 wire service at the main panel the grounds and neutrals would have to tie or the ground fault path wouldn`t trip the breaker. Did I totally miss something.was it a type o.

2014 / 2011 NEC & Related Books and Study Guides
#91200 - 01/04/05 10:01 AM Re: Sub panel
electricman2 Offline

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
I believe that either it was misstated in the discussion or you misread it but in the service equipment the EGC's and the service equipment enclosure are bonded to the grounded service conductor (i.e. the neutral). This provides the fault clearing path.

#91201 - 01/04/05 03:51 PM Re: Sub panel
Physis Offline

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
Do you mean:

[1] neutral
[2] (red) leg
[3] (black) leg
[4] Grounding conductor

The service does not provide a grounding conductor. That's why the service has only three conductors. The GEC at the service is where the grounding conductor comes from and it can only be connected to the service neutral at one point and that is at the service.
Sam, San Francisco Bay Area

#91202 - 01/04/05 03:53 PM Re: Sub panel
Physis Offline

Registered: 12/28/04
Posts: 85
Loc: Burlingame, Ca. USA
After reading your post again. Did they leave out the main bonding jumper?
Sam, San Francisco Bay Area