The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91141 - 12/31/04 03:10 PM Service Riser
ROSLYN Offline
Member

Registered: 12/31/04
Posts: 20
Loc: Sayville, N.Y., 11782-1108
SERVICE PROBLEM: I have a NEW customer, with a existing service repair, 4 - 100 Amp Meters, with a 100 Riser for Meters 1&2 and another 100 Amp riser for meters 3&4. The Town Required the Past Lic. Electrician to install ( 4 ) 100 Amp Disconnects Below Each Meter. QUESTION: is the riser existing permitted to stay, even when the Disconnects & panels were installed to 100 Amps ? I feel a 2/0 Size is required. And how did the utility approve & lock the meters, and the owner got a Electrical CO for this ???

Also, I may add... All ( 4 ) 100 Amp Disconnects are Grounded to a # 6 Awg, together. & there was NO Bonding found in any meter or disconnect to protect the EMT conduit sleves, and NO Cill plates used. A MESS !!!
QUESTION: After this service Upgrade & repair was done by others, Done Wrong. What would you do ? Rip it all down & start over, or repair the existing mess left by another LICENSED Electrician...

[This message has been edited by Roger (edited 12-31-2004).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#91142 - 12/31/04 04:45 PM Re: Service Riser
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
It may not be wrong.

230.90 Exception 3 allows the total rating of the overcurrent protection to exceed the conductor rating. However the calculated load must be less than the conductor rating.

You did not say the size of the service conductors but you did say 100 amp so a 6 AWG GEC may be the right size. GEC size is based on service conductor size not the service overcurrent protection.

I do not think I would rip this out unless the customer wants to exceed the code minimums.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#91143 - 01/03/05 12:28 PM Re: Service Riser
ROSLYN Offline
Member

Registered: 12/31/04
Posts: 20
Loc: Sayville, N.Y., 11782-1108
Thank you " Iwire " In reguards to 230.90 I found out that the LOCAL Utility overides all
NEC tables for services. They require Full size
Feeders for service entrance ( 310.16 ) - Residential ( 2 Gang Meter ) 100/100 needs a
2/0 size riser. Not approved # 4 based on 230.90 Calc. loads, as per my posting problem.
Thanks again.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals