The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 275 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91137 - 12/31/04 11:35 AM Unspliced EGC for pool light
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
What are we using for the splicing of the EGC for the pool lights when an outlet box enclosing a switch is part of the circuit?
George Little

2014 / 2011 NEC & Related Books and Study Guides
#91138 - 12/31/04 12:35 PM Re: Unspliced EGC for pool light
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
I am curious about this myself. The code says "the equipment grounding conductor shall be permitted to terminate on grounding terminals on the transformer, ground-fault circuit interrupter, clock-operated switch enclosure, or an outlet box used to enclose a snap switch."
When I did my pool I ended up with a second unspliced EGC to the listed J box and ran a regular one to the box with the switch and GFCI receptacle. I suppoose you could loop the wire through the ground terminals on the box and switch unspliced but I am not sure how you can splice on a single screw.

A related question, if there is room in a box, can you use a regular "busbar" kit like you use in a panel for your grounding connections? I have seen it and I let it go because it seemed better that a cludge of wires under a wirenut but I doubt it is used as listed and per manufacturer's instructions. (there goes that "L" word again)
It really does make a neater job in one of those 3 and 4 gang boxes.
Greg Fretwell

#91139 - 01/01/05 09:16 PM Re: Unspliced EGC for pool light
mhulbert Offline

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
I use a small busbar kit in jboxes all the time. I like it when you have 6+ EGC coming in, it's better than putting a bunch of blue wirenuts together. As far as listing, I read the directions in one of the square D kits, and it said that if the enclosure has no holes to attach said bar, drill them out and attach the bar. It does not list what enclosures this can be used in. I think that you could argue this as being listed to use in a gutter or box.

Besides, it really is a nicer, more reliable way to do it.


#91140 - 01/02/05 06:16 AM Re: Unspliced EGC for pool light
Redsy Offline

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Look at these:

They include a busbar to splice the grounds, and since you can install circuit breakers for the disconnect means, a light switch and the (required) GFCI receptacle right on them, they greatly reduce labor time in most cases.

[This message has been edited by Redsy (edited 01-02-2005).]