#9110 - 04/17/02 03:46 PM meter base placement
Derington Offline
Junior Member
Registered: 04/17/02
Posts: 2
Would someone please tell me the proper placement for a meter base for an underground service to a mobile home. My electrician is out of town for a week. So we bought a 200 amp meterbase already made up for an underground service. I called him on his cell and he told me he thought it had to be 1'-0 (Is that min or max?)from the trailer and 6'-0 high. That don't sound right to me. Would someone please verify? We have to get this set for the EPB to come out and run the service cable. This is for Hamilton County, Tennessee

Thanks!!
DD
Top
Work Gear for Electricians and the Trades
#9111 - 04/17/02 04:45 PM Re: meter base placement
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
550-23. Service Equipment
(a) Mobile Home Service Equipment.
The mobile home service equipment shall be located adjacent to the mobile home and not mounted in or on the mobile home. The service equipment shall be located in sight from and not more than 30 ft (9.14 m) from the exterior wall of the mobile home it serves. The service equipment shall be permitted to be located elsewhere on the premises, provided that a disconnecting means suitable for service equipment is located in sight from and not more than 30 ft (9.14 m) from the exterior wall of the mobile home it serves. Grounding at the disconnecting means shall be in accordance with Section 250-32.

Remember the supply cord

550-5. Power Supply
(d) Overall Length of a Power-Supply Cord.
The overall length of a power-supply cord, measured from the end of the cord, including bared leads, to the face of the attachment plug cap shall not be less than 21 ft (6.4 m) and shall not exceed 36½ ft (11.13 m). The length of the cord from the face of the attachment plug cap to the point where the cord enters the mobile home shall not be less than 20 ft (6.1 m).

Best Regards,
Doc

[This message has been edited by The Watt Doctor (edited 04-17-2002).]
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
#9112 - 04/17/02 05:03 PM Re: meter base placement
Derington Offline
Junior Member
Registered: 04/17/02
Posts: 2
Thank You Very Much!
It measures 8'-8 from the bottom of the pole to the center of the meter and the ground wire stops about a foot from the bottom of the pole. Should I set it so the center of the meter is between 5 and 6 ft from ground level?

Thanks!!
DD
Top
#9113 - 04/17/02 07:13 PM Re: meter base placement
Chris Rudolph Offline
Member
Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
Most power companies want the meter to be 4 to 6 feet above grade.

Chris
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals