The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/08/16 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 214 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#91083 - 12/29/04 05:42 PM Pool motor bonding
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Does a residential pool motor need to be bonded from the motor to the panel? Or can it be bonding at a water pipe or another closer place. #8 minumum required I believe also, correct?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2014 / 2011 NEC & Related Books and Study Guides
#91084 - 12/29/04 06:33 PM Re: Pool motor bonding
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Read article 680 carefully.

Top
#91085 - 12/29/04 07:54 PM Re: Pool motor bonding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The pool motor (lights etc) gets "grounded" to the panel via the equipment grounding conductor in the circuit feeding it. Pool equipment also gets "bonded" to the pool shell and all other parts of the equipotential grid with a #8 solid copper. That includes pool steel, deck steel, underwater light forming shells and any piece of metal bigger than the palm of your hand within 5' of the water's edge
_________________________
Greg Fretwell

Top
#91086 - 12/29/04 08:22 PM Re: Pool motor bonding
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
But does a separate #8 ground wire have to go back to the panel from the motor, or water pipe?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#91087 - 12/29/04 08:53 PM Re: Pool motor bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
 Quote:
But does a separate #8 ground wire have to go back to the panel from the motor, or water pipe?
No, the items in gfretwell's post get connected together, but it does not have to go anywhere else.

Bill

[This message has been edited by Bill Addiss (edited 12-29-2004).]

Top
#91088 - 12/30/04 09:14 AM Re: Pool motor bonding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Grounding happens via the EGC in the wiring method supplying the motor. In the case of the light that EGC shall also be made "without joint or splice". (from the listed pool J box to the panel with the only place a splice is allowed is in another listed J box or on a terminal bar in the timer/switch).
The pool bonding grid will get grounded via these paths but that is not the intent. The bonding grid is only to ensure that there is no voltage shift between anything you can touch from the pool. In real life I doubt there is a better grounding electrode at your house than a concrete inground pool but again that is not the intent.
_________________________
Greg Fretwell

Top
#91089 - 12/30/04 10:04 AM Re: Pool motor bonding
stevenbohrer Offline
Junior Member

Registered: 12/29/04
Posts: 6
There's a little history to this post in the 100A Subpanel thread, but this thread seemed more appropriate.

To recap:

I have a pool contractor that is replacing existing pool equipment. There is no connection between the pool bond and the panel equipment ground (at least I can't find one). Neither is there an accessible connection point to the pool bond. In 680.26(B)(4), the 2nd paragraph describes bonding provisions for a replacement pump. It specifically says "where there is no connection between the swimming pool bonding grid and the quipment grounding system for the premises, this bonding conductor sall be connected to the equipment grounding conductor of the motor circuit."

Am I missing something? Does code require I bond the pump to the equipment ground (with solid 8 AWG), or do I have to chip out concrete and bond to the pool/patio rebar?

FWIW, the equipment is not within 5' of the pool edge.

Cheers,

Steve

Top
#91090 - 12/30/04 10:56 PM Re: Pool motor bonding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
They should have brought an 8ga bonding conductor from the pool grid to the pump. Are you sure it isn't there in the grass somewhere? If there is a screen cage there should be a stub out to bond it there too.
If they buy a double insulated pump you don't need the bond conductor.
_________________________
Greg Fretwell

Top
#91091 - 12/31/04 09:20 AM Re: Pool motor bonding
stevenbohrer Offline
Junior Member

Registered: 12/29/04
Posts: 6
The area around the pumps is clear, so I think this is just one more code violation in the house (I've already found many others). There is a bond point on the pump, so I don't think it's double insulated.

So as I read the code, in this scenario, I can use 8AWG to bond the pump to the equipment panel instead of chipping concrete?

Top
#91092 - 12/31/04 10:00 AM Re: Pool motor bonding
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Stephen, are you saying there is no EGC (green or bare conductor) in the conduit or cable feeding the pump?

Running a #8 to the panel is not bonding the pool surfaces and equipment to achieve "Equipotential"


Roger

Top