The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Son of Sparky
by HotLine1
Yesterday at 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
HotLine1 6
ghost307 5
sparky 4
Who's Online
0 registered (), 107 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91064 - 12/27/04 06:28 AM physical damage?
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
Wiring a detached garage. UNtil now I didn`t realize they were going to leave studs open un finished I set boxes out 1/2 inch for sheet rock will this fly for inspection I`m planning on calling tommorrow. Just wanted a heads up. I used plactic boxes nm cable stapled as normal. Hope I don`t have to rip it out.

2014 / 2011 NEC & Related Books and Study Guides
#91065 - 12/27/04 09:23 AM Re: physical damage?
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I've seen this go both ways. Some inspectors will maintain that your wiring method is for consealed wiring. The boxes you've used are for consealed wiring. The code allows NM cable for consealed and exposed installation (334.10(A). The issue could be physical protection . Some inspectors don't approve horizontal NM cable in wall studs because of potential storage of things and hanging of things on the cable. That same inspector will allow NM cable in the floor joist in the basement. Must be a double standard. Naw, Inspectors don't have double standards.
George Little

#91066 - 12/27/04 11:55 AM Re: physical damage?
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
I am with George here, the only real hazard I see is if your NM doesn't "closely follow the building finish". The box sticking out may be ugly but it is not a violation. When your customer's wife does talk him into finishing the room it may actually prevent a hazard.
Greg Fretwell