Hi,
I know that 250.66 covers the GEC for water pipes etc. but what about just bonding the copper piping where the waterline is pvc from the curb to the main valve inside the dwelling?

Can I use a #6 to bond this or do I need a #4?

200A with 4/0 AL

I already have dual ground rods installed.

thanks

Greg
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#91022 - 12/22/04 01:00 PM Re: Bonding CW & HW Piping
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't see an article that allows you to use anything but 250.66. Even if you try to use the logic of 250.104(A)(2) you are still stuck with the fact that it only applies to multifamily. I do see the logic but it is easier to make folks happy by following the letter of the code. ROPs are open if you want to add single family to 250.104
_________________________
Greg Fretwell
Top
#91023 - 12/22/04 02:34 PM Re: Bonding CW & HW Piping
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
#4
_________________________
Ryan Jackson,
Salt Lake City
Top
#91024 - 12/22/04 03:15 PM Re: Bonding CW & HW Piping
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
I can use #4 because the work is still being roughed-in but I was just curious because the piping is NOT being used as a GEC it is connecting to a EGC is it not?

Then this would be based on the largest ocpd which in this case would be a 30A for a water heater.

Or am I doing something else?

I guess then there is no way you can EVER connect to the CW/HW piping with a ground other than a #4, #6 and or a #8 solid for bonding whirlpool tub pumps?

Glad I asked!

thanks for the replies.

-regards
greg



[This message has been edited by mustangelectric (edited 12-22-2004).]
_________________________
Electricity has no respect for ignorance!
Top
#91025 - 12/23/04 03:03 AM Re: Bonding CW & HW Piping
shortcircuit Offline
Member
Registered: 06/27/04
Posts: 608
Loc: massachusetts
You must BOND the interior metal water piping system based on table 250.66 according to 250.104(A)(1) EVEN if the building is fed with PVC water pipe.

Exsample: If a one family dwelling has a 400 amp service that is fed with 600MCM AL service entrance conductors, then the bond to the metal water piping must be 1/0 copper based on table 250.66

Well, if the dwelling is completely piped in PVC water pipe, then there isn't anything to bond as instructed by 250.104(A)(1)

Other metal piping systems must be bonded according to table 250.122 useing the rating of the OCPD likely to energize the piping.

Exsample:The dwelling's water pipe is all PVC...but the plumber installs the forced hot water piping with copper from the oil fired boiler which is fed by a 15 amp OCPD, well then the equipment grounding conductor run with the circuit conductors is what you would use for the bond(#14).

If that whirlpool tub is fed with copper water pipe,then bond the motor to the piping under the tub with #8 solid.If it is fed with PVC pipe then there isn't anything to bond.

shortcircuit
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals