The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Members: Non-Members: Did you know?
by Admin
Today at 02:34 PM
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 36
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (Admin), 83 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#91008 - 12/21/04 07:11 PM 2005 Code Change
HoseB611 Offline
Member
Registered: 12/24/02
Posts: 16
Can someone explain to me the change to 210.12 Arc Fault Circuit-Interrupter Protection, "require that all dwelling unit bedroom branch circuit AFCI protection devices must be listed as a "combination Type AFCI", effective Jan. 1 2008." First of all I have never heard of the "combination type AFCI, and secondly the way I understand it is all 120V branch circuits being supplying 15 or 20A outlets in bedrooms must be AFCI protected. Does that include the lighting outlets, fan outlets, and recepticle outlets? Need clarification please..
Top
2017 / 2014 NEC & Related Books and Study Guides
#91009 - 12/21/04 07:32 PM Re: 2005 Code Change
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
The two biggest differences between the AFCI's is that the combination type is supposed to trip at 5 miliamps of current as opposed to 75, and the combination type is also supposed to detect arc faults after the outlet, such as cord and plug connected equipment.

As for your other questions, yes, all outlets in the bedroom (120 volt, 15/20 amp) are to be protected. This includes receptacles, light fixtures, smoke detectors, etc...
_________________________
Ryan Jackson,