#90937 - 12/18/04 08:23 AM Water Heater Connections
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
I used to just stub out a 10/2 w grnd at the water heater and bond the cold water.

What is the best way to do it now?

Do I need to run flex over to the heater itself?

Do I need to bond the hot and cold together back to the panel?

Thanks for any comments.

-regards

Greg
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#90938 - 12/18/04 08:39 AM Re: Water Heater Connections
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
They want to see a disconnect around here and that is usually where the electrician stops, although he still "owns" the wire going to the water heater if there is a violation. I see them run in everything from just Romex to FMC, MC or SealTite.
I haven't seen metal water pipe in so long I tend to forget about bonding
_________________________
Greg Fretwell
Top
#90939 - 12/18/04 08:45 AM Re: Water Heater Connections
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
yes that is why I am asking because what used to be ok may not be the norm nowadays...I havent heard of a disco being required at the heater itself. This is not a code requirement is it?

I will probably just use my old standard...stub out the 10/2 wgrnd and use a romex connector toconnect it to the heater itself.

See any problem with that?

Most everything around here is Copper.

-regards

Greg
_________________________
Electricity has no respect for ignorance!
Top
#90940 - 12/18/04 08:53 AM Re: Water Heater Connections
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Greg,

A disconnect may be required, depending on where the water heater is located in relationship to the panel that feeds it. A water heater is an appliance, so check out 422.31(B)

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#90941 - 12/18/04 08:59 AM Re: Water Heater Connections
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Almost everything we wire needs a disconnecting means within sight.

There are some exceptions and also sometimes ways around it with breaker locks.

As Tom pointed out check out 422.31(B) for water heater.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#90942 - 12/18/04 09:07 AM Re: Water Heater Connections
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
The water heater certainly exceeds the 300w limit. The circuit breaker is NOT within sight but it can be locked in the open position with a breaker lock-out.

Should I just put a non fused disco at all water heaters and forget it? What is the norm anymore?

Thanks for the code ref.

-regards

Greg
_________________________
Electricity has no respect for ignorance!
Top
#90943 - 12/18/04 11:24 AM Re: Water Heater Connections
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
Breaker locks are approved here and are cheaper than a disco.
_________________________
John
Top
#90944 - 12/18/04 05:04 PM Re: Water Heater Connections
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
If I was the AHJ on an inspection for a water heater, I would accept a breaker padlock device manufactured by the same company that made the breaker/panelboard.

Many mobile/manufactured homes have an electric water heater & every one that i have looked at has a padlock attachment on the breaker. This makes HUD happy & so a similar installation in a dwelling should satisfy any AHJ you deal with, but it is always best to ask if you aren't sure.

You could use one of those $8 pull out air conditioner disconnects just to CYA, but IMO, you'd be wasting $8 & some time.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals