#90928 - 12/18/04 06:42 AM Single-phase cord-and-plug-connected room air conditioners?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Does anyone know if these are available yet?

Quote:
440.65 Leakage Current Detection and Interruption (LCDI) and Arc Fault Circuit Interrupter (AFCI).

Single-phase cord-and-plug-connected room air conditioners shall be provided with factory-installed LCDI or AFCI protection.

The LCDI or AFCI protection shall be an integral part of the attachment plug or be located in the power supply cord within 300 mm (12 in.) of the attachment plug.
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#90929 - 12/18/04 07:21 AM Re: Single-phase cord-and-plug-connected room air conditioners?
Ron Offline
Member
Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
_________________________
Ron
Top
#90930 - 12/18/04 06:27 PM Re: Single-phase cord-and-plug-connected room air conditioners?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Thanks Ron, I have seen that product at trade shows. The rule calls for "factory installed ...." so the Fireshield may be what is used. I wondered if the AC units are or will become available with the AFCI, etc., installed. I am sure we wouldn't want to see someone replace the cord on a unit.
_________________________
Joe Tedesco, NEC Consultant
Top
#90931 - 12/18/04 08:33 PM Re: Single-phase cord-and-plug-connected room air conditioners?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
This has been in the code since 2002 but I have never been sure how you enforce it.
Does this mean anyone with a window shaker that preceeds this requirement has to throw it away?
I have never actually seen one. I guess the next time I am in Home Depot I will look at the floor models. Can I red tag the units if the AFCIs aren't there :-)
_________________________
Greg Fretwell
Top
#90932 - 12/21/04 01:48 PM Re: Single-phase cord-and-plug-connected room air conditioners?
tdhorne Offline
Member
Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
What we are talking about is UL listed portable appliances. So if it has a listing mark and there is no evidence of modification it is beyond the inspectors perview.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#90933 - 12/21/04 08:02 PM Re: Single-phase cord-and-plug-connected room air conditioners?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
How do requirements for "plug-in" appliances fit the scope of the NEC?
[quote]90.2 Scope.
(A) Covered. This Code covers the installation of electric conductors, electric equipment, signaling and communications conductors and equipment, and fiber optic cables and raceways for the following:[/quiote]
In my opinion plug-in equipment is "used", not installed. The NEC should stop at the receptacle and let the product safety standards cover the plug-in equipment. If we keep adding rules to cover plug-in equipment the code will soon be a multi-volume book.
Don
_________________________
Don(resqcapt19)
Top
#90934 - 12/21/04 09:08 PM Re: Single-phase cord-and-plug-connected room air conditioners?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
It's what I call "code creep". Immersion detectors on hair dryers have been in the code for a few cycles (also unenforceable). We are going to be inspecting table lamps and clock radios soon.
_________________________
Greg Fretwell
Top
#90935 - 12/22/04 04:22 AM Re: Single-phase cord-and-plug-connected room air conditioners?
George Little Offline
Member
Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Greg- You guys are starting to scare me. It looks like all the people have to do is unplug the questionable equipment and the code is satisfied. What about heat tapes for ice melting? What about portable signs? What about swimming pool equipment? We're suppost to protect the public interest. If I/we don't say something about the non code compliant equipment and they run into trouble with it, they come back and say "Why didn't you tell us"? The attorneys will have a hay day with that one.
_________________________
George Little
Top
#90936 - 12/22/04 09:44 AM Re: Single-phase cord-and-plug-connected room air conditioners?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
"It looks like all the people have to do is unplug the questionable equipment and the code is satisfied."

Is part of the final inspection going to be searching the moving van for unlisted equipment?
I can understand "fixed in place" cord and plug connected being subject to inspection on the final but what can we do about things that the new owner brings with him or buys after the CO? (Window shakers and hair dryers) How is that our business? Are we supposed to be raiding flea markets and looking for listing tags at the Home Depot?
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 110 Guests and 17 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals