#90870 - 12/15/04 05:54 PM SER Cable Sheath Damage
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
I am wondering what to do about a ASER cable that the sheath some how got cut in several places along the middle section of a 50 foot run. It looks like a nail or some sharp edge that was hidden got a hold to it.

I cant reallt tell if the XHHW conductors were just scored or if the insulation was actually cut or not.

I hate to replace the cable if there is an acceptable way to use it.

Thanks for any replies or suggestions.

-regards

Greg
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#90871 - 12/16/04 05:06 AM Re: SER Cable Sheath Damage
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg- Since the outer jacket would not figure in as the electrical insulation on the coductors, I'd remove the outter jacket where it was damaged and inspect the conductor insulation. If the conductor insulation and the uninsulated conductor are are not damaged, I'd use a good grade of plastic tape and tape the cable up and move on.
_________________________
George Little
Top
#90872 - 12/16/04 05:31 AM Re: SER Cable Sheath Damage
sgreany Offline
Member
Registered: 07/18/03
Posts: 26
If there is any question at all, replace it. Ask urself is it worth the risk of the posible consiquenses of better to be safe.
Top
#90873 - 12/16/04 05:32 AM Re: SER Cable Sheath Damage
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
George,
I was thinking that I could do that. The sections that have some cuts are accessible and I was thinking of using a few wraps some 33 on it. The sheath for this cable is very thin and not very durable.

As a matter of fact that is my opinion of all residential wire except UF. It seems to me they would make a tad bit tougher.

Thank you for the comment.

-regards

Greg
_________________________
Electricity has no respect for ignorance!
Top
#90874 - 12/16/04 05:36 AM Re: SER Cable Sheath Damage
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Sgreany,
Thanks for the input. I dont see where the conductors themselves were damaged. I think the code allows us to build the insulation back up to the original level and as long as there is no METAL lost on the conductor itself there current carrying capacity of the cable is as good as anything on the shelf.

I will put some 77 on first.

Safety is always my main concern.

-regards

greg
_________________________
Electricity has no respect for ignorance!
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals