The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 185 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90837 - 12/15/04 09:35 AM 2 wires on breaker?
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Hey guys where do I find where its permissable to have 2 wires on a breaker.Listing for the device in the white book?Here`s why I ask I always wire a couple of bed rooms on a afci and bring the circits to panel and place both on same breaker reason is I can easily separate for trouple shooting and if its something I can`t do at the time I can at least have the other room working real quick by moving to another afci.New code inforcement guy wants to see why I can other than me saying it has a place for 2 wires on the breaker.I really can`t find the justification for it.Thanks in advance

Top
2014 / 2011 NEC & Related Books and Study Guides
#90838 - 12/15/04 10:12 AM Re: 2 wires on breaker?
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
I believe Square D QO will accept 2 conductors, there may be others. Consult manufacturer. Why not just pigtail in panel?
_________________________
John

Top
#90839 - 12/15/04 12:09 PM Re: 2 wires on breaker?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
On the QO it is right on the breaker. Look at the tiny label in the wiring recess. Bring your glasses ;-)
_________________________
Greg Fretwell

Top
#90840 - 12/15/04 03:32 PM Re: 2 wires on breaker?
energy7 Offline
Member

Registered: 06/10/02
Posts: 58
Loc: Oxnard, CA, USA
I usually find it on the listing label on the panelboard cover. (Where it's upside down, and in small print. So use your glasses and crank your head around.)
Every brand I've seen recently allows double lugging only on the grounding conductors. Hots and Neutrals (That's "ungrounded and grounded conductors", sorry!) are singles.

Top
#90841 - 12/15/04 04:32 PM Re: 2 wires on breaker?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Energy7, the information on the panel or panel cover, doesn't directly address the breakers.

For an example go to this Homeline breaker link, and scroll down to the Circuit Breaker Wire Sizes, take note of the (2) in the conductors listed for breakers 10 thru 30 amps.

Reel-Break, now for the bad news if you are using SQ D QO breakers (I would contact SQ D for clarification) in the QO series You will see the AFCI's are only listed for one conductor.

The other manufacturers may list their AFCI's for two conductors, you can contact them for this info, I have always found them willing to help.

Roger

Top
#90842 - 12/19/04 04:17 PM Re: 2 wires on breaker?
wayne Offline
Member

Registered: 04/04/01
Posts: 55
Loc: NC
Hi Reel break,
I can understand the reason why you like to do that, What I do around here, since there is one wire per breaker I make a yoke ( splice) whin a few inches of the breaker in question. I have not seen it in the code that would allow you to do it otherwise, unless the equipment is designed for it. Hope this will help, thought I would just drop a little input. later

Top
#90843 - 12/20/04 06:21 AM Re: 2 wires on breaker?
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Thanks guys for the responces.Hey Roger thanks I was useing the qo for this one.

Top