#90829 - 12/12/04 03:39 PM 2 ungrounded conductors / 1 means of protection
rkidd Offline
Junior Member
Registered: 12/12/04
Posts: 2
Loc: Atlanta, Ga. USA
I recently cited a double tap (two ungrounded conductors terminating on one 20A breaker) in a service panel as a code violation, but when challanged on it, I can not find it in either the 1999 or the 2002 NEC. I fell like an idiot. Can someone help me out here?
_________________________
Ray
Top
2017 / 2014 NEC & Related Books and Study Guides
#90830 - 12/12/04 03:44 PM Re: 2 ungrounded conductors / 1 means of protection
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
110.3(B) or last sentence of 110.14(A)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#90831 - 12/12/04 05:14 PM Re: 2 ungrounded conductors / 1 means of protection
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
rkidd,

Before citing "double taps" be sure that the breaker is not designed for 2 terminations.
The double tap was commonly cited when I was doing real eatate work. However, some designs such as the "pressure plate" type of termination (Square D uses this) allow 2 conductors of the same size to be terminated on the breaker.
Top
#90832 - 12/12/04 05:15 PM Re: 2 ungrounded conductors / 1 means of protection
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
This is one of those things that a lot of people in the trade assume is always a code violation. Not necessarily. It is completly dependent on whether or not the circuit breaker is listed for one or two wire. Many 15 and 20Amp circuit breakers are in fact listed to accomodate 2 wires. Reference the link below from the web site of Mike Holt (who probably has more credability than me
http://www.mikeholt.com/technical.php?id=nec/unformatted/Jan_ECM&type=u&title=NEC%20-%20Question/Answers%20(1-4-2K)
Top
#90833 - 12/12/04 09:39 PM Re: 2 ungrounded conductors / 1 means of protection
rkidd Offline
Junior Member
Registered: 12/12/04
Posts: 2
Loc: Atlanta, Ga. USA
Thank you all for the speedy replys. With these three answers plus the ref. to the Mike Holt site, I get it. I was barking up the wrong tree thinking I would find something that would say only one branch circuit can be protected by one over current device. Thanks again. Ray
_________________________
Ray
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals