The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90829 - 12/12/04 03:39 PM 2 ungrounded conductors / 1 means of protection
rkidd Offline
Junior Member

Registered: 12/12/04
Posts: 2
Loc: Atlanta, Ga. USA
I recently cited a double tap (two ungrounded conductors terminating on one 20A breaker) in a service panel as a code violation, but when challanged on it, I can not find it in either the 1999 or the 2002 NEC. I fell like an idiot. Can someone help me out here?
_________________________
Ray

Top
2014 / 2011 NEC & Related Books and Study Guides
#90830 - 12/12/04 03:44 PM Re: 2 ungrounded conductors / 1 means of protection
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
110.3(B) or last sentence of 110.14(A)
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#90831 - 12/12/04 05:14 PM Re: 2 ungrounded conductors / 1 means of protection
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
rkidd,

Before citing "double taps" be sure that the breaker is not designed for 2 terminations.
The double tap was commonly cited when I was doing real eatate work. However, some designs such as the "pressure plate" type of termination (Square D uses this) allow 2 conductors of the same size to be terminated on the breaker.

Top
#90832 - 12/12/04 05:15 PM Re: 2 ungrounded conductors / 1 means of protection
Electric Ian Offline
Member

Registered: 02/10/04
Posts: 132
Loc: MA, USA
This is one of those things that a lot of people in the trade assume is always a code violation. Not necessarily. It is completly dependent on whether or not the circuit breaker is listed for one or two wire. Many 15 and 20Amp circuit breakers are in fact listed to accomodate 2 wires. Reference the link below from the web site of Mike Holt (who probably has more credability than me
http://www.mikeholt.com/technical.php?id...wers%20(1-4-2K)

Top
#90833 - 12/12/04 09:39 PM Re: 2 ungrounded conductors / 1 means of protection
rkidd Offline
Junior Member

Registered: 12/12/04
Posts: 2
Loc: Atlanta, Ga. USA
Thank you all for the speedy replys. With these three answers plus the ref. to the Mike Holt site, I get it. I was barking up the wrong tree thinking I would find something that would say only one branch circuit can be protected by one over current device. Thanks again. Ray
_________________________
Ray

Top