#90682 - 12/07/04 09:16 PM Polarity testing
tdhorne Offline
Member
Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
When your plug in tester reads polarity reversal and your wiggy reads 120 volts from ground to neutral and from hot to neutral what two totally different failures can cause this.
--
Tom

[This message has been edited by tdhorne (edited 12-08-2004).]
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
2017 / 2014 NEC & Related Books and Study Guides
#90683 - 12/07/04 09:29 PM Re: Polarity testing
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Open neutral upstream and that may be a bad contact in a GFCI receptacle (covered here several times). You are seeing a back circuit through the downstream load.
_________________________
Greg Fretwell
Top
#90684 - 12/08/04 07:46 AM Re: Polarity testing
John M Caloggero Offline
Junior Member
Registered: 11/25/04
Posts: 8
Loc: Virginia Beach VA
I assume you are taking measurements at the receptacle. The tester is saying you have reversed polarity, that means the neutral and live conductor are reversed. It sounds like the grounded conductor (neutral) is connected to the brass colored terminal to which the live conductor is supposed to be connected, and the live conductor is connected to the white or silver colored terminal to which the grounded conductor (neutral) is to be connected.
Top
#90685 - 12/08/04 12:32 PM Re: Polarity testing
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
John if this is a simple polarity reversal you wouldn't see volts on the brass screw
_________________________
Greg Fretwell
Top
#90686 - 12/08/04 12:51 PM Re: Polarity testing
n1ist Offline
Member
Registered: 02/13/02
Posts: 176
Loc: Malden MA
If you reverse hot and neutral you would see this. If you roll all 3 lines so hot is on silver, ground is on brass, and neutral is on green, you would also see this.
/mike
Top
#90687 - 12/10/04 05:45 PM Re: Polarity testing
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
It's an open neutral, nothing else. Most of the cheap plug in testers will show reverse polarity on an open neutral condition since the neutral is now at 120V potential from upstream load.
Top
#90688 - 12/10/04 05:51 PM Re: Polarity testing
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Sorry I didn't notice you said 120 from hot to neutral. It must be like mike said,simply reverse polarity. Your getting 120 from neutral to grd because your neutral is really a hot.
Top
#90689 - 12/10/04 09:08 PM Re: Polarity testing
tdhorne Offline
Member
Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
How I got the readings described were from a fault from the hot to the Equipment Grounding Conductor with an open in the EGC between the fault and the source.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top
#90690 - 12/11/04 03:52 PM Re: Polarity testing
BigB Offline
Member
Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Tom, did and earlier fault cause the EGC to blow apart, then become energized when the breaker was reset?
Just goes to show how trying to guess a problem without being there can make a fool out of you.
Top
#90691 - 12/12/04 07:01 PM Re: Polarity testing
tdhorne Offline
Member
Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
Quote:
BigB Tom, did and earlier fault cause the EGC to blow apart, then become energized when the breaker was reset?
Just goes to show how trying to guess a problem without being there can make a fool out of you.
So far it appears that the separation of the armor jacket of the old type BX cable caused the fault by cutting into the insulation of the hot conductor.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (dougwells, Admin), 190 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals