The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90632 - 12/06/04 10:02 AM Gutter Sizing
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
I have 18 - 1" conduits that need to go to a gutter.

314.28(A)(1)covers this right? Only #4 and larger though. Anything smaller and it is based on condcutors right?

I guess a gutter that has no terms in it is a pull box?

Are there specific sections that refer to a "Gutter" or is this the same as "Pull Box"?

Thanks for any replies.

-regrads

MUSTANG


[This message has been edited by mustangelectric (edited 12-06-2004).]
_________________________
Electricity has no respect for ignorance!

Top
2017 / 2014 NEC & Related Books and Study Guides
#90633 - 12/06/04 02:28 PM Re: Gutter Sizing
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
See Article 366 and Article 376.

You are allowed a 20% fill and up to 30 current carrying conductors. If you exceed 30 conductors, you have to do the derating per table 310.15(B)(2)(a)

Essentially, they are the same thing, they just differ in how they are used.

Tom

[This message has been edited by Tom (edited 12-06-2004).]

[This message has been edited by Tom (edited 12-06-2004).]
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#90634 - 12/07/04 12:24 PM Re: Gutter Sizing
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
312.6(A) cover gutters too right?

Thanks for the help.

-regards

Mustang
_________________________
Electricity has no respect for ignorance!

Top
#90635 - 12/07/04 02:35 PM Re: Gutter Sizing
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Yes Mustang, 312.6 applies too. There was a change in the 2005 to address this more clearly, stating that the "one wire per terminal" column is to be used, even if you have conductors in parrallel.
_________________________
Ryan Jackson,
Salt Lake City

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals