#90632 - 12/06/04 10:02 AM Gutter Sizing
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
I have 18 - 1" conduits that need to go to a gutter.

314.28(A)(1)covers this right? Only #4 and larger though. Anything smaller and it is based on condcutors right?

I guess a gutter that has no terms in it is a pull box?

Are there specific sections that refer to a "Gutter" or is this the same as "Pull Box"?

Thanks for any replies.

-regrads

MUSTANG


[This message has been edited by mustangelectric (edited 12-06-2004).]
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#90633 - 12/06/04 02:28 PM Re: Gutter Sizing
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
See Article 366 and Article 376.

You are allowed a 20% fill and up to 30 current carrying conductors. If you exceed 30 conductors, you have to do the derating per table 310.15(B)(2)(a)

Essentially, they are the same thing, they just differ in how they are used.

Tom

[This message has been edited by Tom (edited 12-06-2004).]

[This message has been edited by Tom (edited 12-06-2004).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#90634 - 12/07/04 12:24 PM Re: Gutter Sizing
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
312.6(A) cover gutters too right?

Thanks for the help.

-regards

Mustang
_________________________
Electricity has no respect for ignorance!
Top
#90635 - 12/07/04 02:35 PM Re: Gutter Sizing
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yes Mustang, 312.6 applies too. There was a change in the 2005 to address this more clearly, stating that the "one wire per terminal" column is to be used, even if you have conductors in parrallel.
_________________________
Ryan Jackson,
Salt Lake City
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals