#90572 - 11/30/04 08:58 AM NM in conduit
energy7 Offline
Member
Registered: 06/10/02
Posts: 58
Loc: Oxnard, CA, USA
A comment in the "horse barn" thread has stirred this question.
Can you run NM in conduit for any significant distance. My understanding of 336-6 (and now 334-15) is that conduit protection is used in short runs for specific hazards.
Because NM is a cable assembly and not just conductors, running it in conduit is "mixing wiring methods", and you're subject to overheating.
Top
2017 / 2014 NEC & Related Books and Study Guides
#90573 - 11/30/04 09:10 AM Re: NM in conduit
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
This has been cleared up in the 2005 NEC.

It is specifically allowed in the .22 sections of the conduit articles if the particular cable article doesn't prohibit it.

Roger
Top
#90574 - 11/30/04 09:39 AM Re: NM in conduit
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't see how heating is considered an issue at all, code wise. You derate the same in 1/2" conduit as you do in 4" for the same conductor fill. A piece of Romex in "free air" EMT will certainly run cooler than it would buried in insulation in an attic.
_________________________
Greg Fretwell
Top
#90575 - 11/30/04 09:50 AM Re: NM in conduit
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
the .22 additions only point out rules that always existed. Basically you use the widest dimension of an oval cable as the diameter when computing fill. That is because when you get a twist in it the widest dimension becomes the diameter.
_________________________
Greg Fretwell
Top
#90576 - 11/30/04 08:07 PM Re: NM in conduit
John Steinke Offline
Member
Registered: 04/03/01
Posts: 518
Loc: Reno,Nv., USA
Romex is listed as a 60 degree assembly.
The THHN wire inside romex is listed as a 90 degree wire.

By putting romex in pipe, you are throwing away 30 degrees of de-rating, before you do anything else.

Also, the inside of conduit can sometimes be considered a wet location; romex is not allowed in wet locations.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 65 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals