The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
39 minutes 26 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 234 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90567 - 11/30/04 07:25 AM got a new one for you!!!!
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
What do you think of being told you can`t place a recessed can in a ceiling with no attic area. He maintains I can only install a old work can there.Not one with rails installed. He maintains no accses to juction box. Never heard this one.But I see a point almost but it can be taken out but not easily.Heck we do it all the time down stairs cans.Is there any justification for this.

Top
2014 / 2011 NEC & Related Books and Study Guides
#90568 - 11/30/04 08:13 AM Re: got a new one for you!!!!
George Offline
Member

Registered: 02/23/02
Posts: 380
The rails are just a convience for installing.

You can remove the assembly thru the light hole to gain access to the junction box.

Top
#90569 - 11/30/04 01:23 PM Re: got a new one for you!!!!
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
Another day another dope. Is this "He" claiming to be an inspector.

Top
#90570 - 11/30/04 01:46 PM Re: got a new one for you!!!!
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
410.67 Wiring.
(A) General. Conductors that have insulation suitable for the temperature encountered shall be used.
(B) Circuit Conductors. Branch-circuit conductors that have an insulation suitable for the temperature encountered shall be permitted to terminate in the luminaire (fixture).
(C) Tap Conductors. Tap conductors of a type suitable for the temperature encountered shall be permitted to run from the luminaire (fixture) terminal connection to an outlet box placed at least 300 mm (1 ft) from the luminaire (fixture). Such tap conductors shall be in suitable raceway or Type AC or MC cable of at least 450 mm (18 in.) but not more than 1.8 m (6 ft) in length.

This has been in the Code in one form or another for quite a while. The placement of the outlet box one foot away was for maintenance.
The 6 feet (used to be 4-6 feet)of suitable raceway allowed you to drop the can out of the ceiling and get it out of your face to get in to the J box one foot away to service the branch circuit conductors. Another theory was the (4) to 6' that used to be required (before pre-wired fixtures I think 1996 or 99) allowed the fixture wires to cool before they contacted the old 60 degree Cel. wiring at the branch circuit J box . The old recessed cans used to come with a snap on J box no pre wire no fixture wire.


BTW unless otherwise listed your installation should be acceptable
Charlie

[This message has been edited by cpal (edited 11-30-2004).]

Top
#90571 - 12/06/04 04:47 PM Re: got a new one for you!!!!
HLCbuild Offline
Member

Registered: 12/05/04
Posts: 206
Loc: Herndon,Va USA
Reel-Break,

I was tripped up on this one some years back. It was with a recessed fixture, rated for thru-branch wiring, but it had a small opening. There is a problem with the UL listing of the fixture. UL list recessed fixtures with an opening smaller than 6" to have its junction box very close to the opening to be rated for thru branch wiring. I forget the equation, but it has to do with adding the distance horizontally and vertically that the bos is located from the opening and comparing this amount to the diameter of the opening. If you need it, I'll look it up

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals