#90495 - 11/23/04 04:13 PM SE Rated Switch/Disco  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Is there ANY requirement in the NEC that requires a switch or disconnect to be Service Entrance rated?

Please quote the article if known.

Thanks for any replies.

-regards

Mustang

[This message has been edited by mustangelectric (edited 11-23-2004).]


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#90496 - 11/23/04 04:39 PM Re: SE Rated Switch/Disco  
CharlieK  Offline
Member
Joined: Mar 2003
Posts: 21
Baltimore. Md. U.S.A.
How about when it is used for SERVICE EQUIPMENT? I have always used a service equipment rated disconnect or enclosed breaker as the first throw on a service. Most discos that are not service equipment rated have no means of grounding the neutral.


#90497 - 11/23/04 04:40 PM Re: SE Rated Switch/Disco  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
2002 NEC See 230.66, 110.9 & 110.10


Joe Tedesco, NEC Consultant

#90498 - 11/23/04 05:05 PM Re: SE Rated Switch/Disco  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Try discussing this question with the utility company. I was unable to find the name of the local electrical inspector.

Electric Department
Electric Utilities Manager
Rex Garrett
(479) 271-3135
rgarrett@bentonvillear.com

Electric Utilities Assistant Manager
Paul Kellenbarger
over Technical Design
(479) 271-3159
pkellenbarger@bentonvillear.com

Electric Utilities Assistant Manager
Donnie Johnson
over Construction
(479) 271-5985
djohnson@bentonvillear.com


Joe Tedesco, NEC Consultant

#90499 - 11/23/04 05:47 PM Re: SE Rated Switch/Disco  
cpal  Offline
Member
Joined: May 2004
Posts: 162
Cohasset MA
you might consider the requiremnt in 225 regarding the marking of equipment, in addition to those references previously mentioned

225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.

Charlie

[This message has been edited by cpal (edited 11-23-2004).]


#90500 - 11/23/04 07:20 PM Re: SE Rated Switch/Disco  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Thanks for the replies. I should have said a SWITCH or DISCO used as the Main.

I appreciate the code references.

-regards

Mustang


[This message has been edited by mustangelectric (edited 11-23-2004).]


Electricity has no respect for ignorance!

#90501 - 12/07/04 12:33 PM Re: SE Rated Switch/Disco  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
I think Art 110.9 and 110.10 cover this.

Thanks

Mustang


Electricity has no respect for ignorance!

#90502 - 12/08/04 01:21 AM Re: SE Rated Switch/Disco  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.

I would think that about covers it.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#90503 - 12/08/04 09:01 AM Re: SE Rated Switch/Disco  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Yes that would cover it. Why are inspectors so adamate about getting the SE rating of a disco sold to the public?

IS there a big counterfit market? Don't manufacturers have to meet this when they design these devices?

The inspector I am dealing with sent a comment letter asking to verify compliance with 110.9 and 110.10.

Thanks for pointing those out and the great replies.

-regards

Mustang


Electricity has no respect for ignorance!


Member Spotlight
RonKipperDatacom
RonKipperDatacom
Kansas City, KS
Posts: 30
Joined: January 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7990 MB (Peak: 0.9664 MB) Zlib enabled. Server Time: 2017-03-26 03:29:12 UTC