The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 185 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90495 - 11/23/04 12:13 PM SE Rated Switch/Disco
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Is there ANY requirement in the NEC that requires a switch or disconnect to be Service Entrance rated?

Please quote the article if known.

Thanks for any replies.

-regards

Mustang

[This message has been edited by mustangelectric (edited 11-23-2004).]
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#90496 - 11/23/04 12:39 PM Re: SE Rated Switch/Disco
CharlieK Offline
Member

Registered: 03/10/03
Posts: 23
Loc: Baltimore. Md. U.S.A.
How about when it is used for SERVICE EQUIPMENT? I have always used a service equipment rated disconnect or enclosed breaker as the first throw on a service. Most discos that are not service equipment rated have no means of grounding the neutral.

Top
#90497 - 11/23/04 12:40 PM Re: SE Rated Switch/Disco
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
2002 NEC See 230.66, 110.9 & 110.10
_________________________
Joe Tedesco, NEC Consultant

Top
#90498 - 11/23/04 01:05 PM Re: SE Rated Switch/Disco
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Try discussing this question with the utility company. I was unable to find the name of the local electrical inspector.

Electric Department
Electric Utilities Manager
Rex Garrett
(479) 271-3135
rgarrett@bentonvillear.com

Electric Utilities Assistant Manager
Paul Kellenbarger
over Technical Design
(479) 271-3159
pkellenbarger@bentonvillear.com

Electric Utilities Assistant Manager
Donnie Johnson
over Construction
(479) 271-5985
djohnson@bentonvillear.com
_________________________
Joe Tedesco, NEC Consultant

Top
#90499 - 11/23/04 01:47 PM Re: SE Rated Switch/Disco
cpal Offline
Member

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
you might consider the requiremnt in 225 regarding the marking of equipment, in addition to those references previously mentioned

225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.

Charlie

[This message has been edited by cpal (edited 11-23-2004).]

Top
#90500 - 11/23/04 03:20 PM Re: SE Rated Switch/Disco
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Thanks for the replies. I should have said a SWITCH or DISCO used as the Main.

I appreciate the code references.

-regards

Mustang


[This message has been edited by mustangelectric (edited 11-23-2004).]
_________________________
Electricity has no respect for ignorance!

Top
#90501 - 12/07/04 08:33 AM Re: SE Rated Switch/Disco
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
I think Art 110.9 and 110.10 cover this.

Thanks

Mustang
_________________________
Electricity has no respect for ignorance!

Top
#90502 - 12/07/04 09:21 PM Re: SE Rated Switch/Disco
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.

I would think that about covers it.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#90503 - 12/08/04 05:01 AM Re: SE Rated Switch/Disco
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Yes that would cover it. Why are inspectors so adamate about getting the SE rating of a disco sold to the public?

IS there a big counterfit market? Don't manufacturers have to meet this when they design these devices?

The inspector I am dealing with sent a comment letter asking to verify compliance with 110.9 and 110.10.

Thanks for pointing those out and the great replies.

-regards

Mustang