#90428 - 11/20/04 09:40 PM Thermal Overload
Sparky_1 Offline
Member
Registered: 11/20/04
Posts: 14
We have 3 3 phase 3 HP fan motors that are
continuous duty.
Can we use cord and plug and the breaker
to operate the motors? or do we have to
use a overload section on each motor?

Thanks,
Sparky_1
Top
2017 / 2014 NEC & Related Books and Study Guides
#90429 - 11/21/04 07:03 AM Re: Thermal Overload
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Most 3 phase motors do not have built in overload protection. You have to install an overload device in each conductor & this is usually done with a motor starter. See 430.32

As for using the cord & plug connection, that will require a horsepower rated receptacle and a horsepower rated cord cap.430.109(F)

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#90430 - 11/21/04 07:51 AM Re: Thermal Overload
Sparky_1 Offline
Member
Registered: 11/20/04
Posts: 14
Thanks for the information Tom
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals