#90420 - 11/20/04 02:26 PM Sign and Fountains
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
How close to a fountian can I install a permanently installed sign? We are talking not inthe fountian but outside the fountian.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#90421 - 11/20/04 02:48 PM Re: Sign and Fountains
russ m Offline
Member
Registered: 02/22/03
Posts: 169
Loc: Burbank,IL,USA
I can't see why it can,t be next to the fountain, 680.6
Top
#90422 - 11/20/04 02:57 PM Re: Sign and Fountains
russ m Offline
Member
Registered: 02/22/03
Posts: 169
Loc: Burbank,IL,USA
680.22(B)(1) and(3) seem to apply also, If we are talking about a sign with lights in or on it.
Top
#90423 - 11/20/04 06:01 PM Re: Sign and Fountains
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Russ, I looked at your code references and I think that they wouldn't apply since that Section (Section II.) is dealing about Permanently Installed Pools. I'm looking at Section V. which deals with Fountains. 680.57(C) deals with Signs and there locations in the fountian and with Portable Signs outside the fountain. Nothing about permanently installed signs outside the fountain. I also didn't find anything in Section I (General) that helped me.

[This message has been edited by George Little (edited 11-20-2004).]
_________________________
George Little
Top
#90424 - 11/20/04 11:06 PM Re: Sign and Fountains
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I have seen signs IN the fountain. Is that close enough? I would apply the 680.57 rules.
If it is just next to the fountain, isn't that simply a "wet location"?
Am I missing something?
Is this a neon sign or just a 120v deal?


[This message has been edited by gfretwell (edited 11-21-2004).]
_________________________
Greg Fretwell
Top
#90425 - 11/20/04 11:42 PM Re: Sign and Fountains
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Greg- this example is hypothetical, I was teaching a class and we were covering Article 680 and a student raised the question. The code covers it if the sign is in the fountain and if the sign is portable and outside the fountain but says nothing if it is permanently installed outside the fountain. Leads one to believe that it can be right next to the fountian with no restrictions or any special bonding or GFCI protection. Go figure??

[This message has been edited by George Little (edited 11-21-2004).]
_________________________
George Little
Top
#90426 - 11/21/04 12:46 PM Re: Sign and Fountains
russ m Offline
Member
Registered: 02/22/03
Posts: 169
Loc: Burbank,IL,USA
George

If there is a pool (doesn't say what kind) associated with the fountain, then part two of 680 would apply.
OK lets say there no type of collection pool.

Part 1 680.6(2) pertains to all electrical equipment within 5ft of the (pool) fountain.

Don't mean to be repettive but thats how I read it.


[This message has been edited by russ m (edited 11-21-2004).]
Top
#90427 - 11/21/04 05:17 PM Re: Sign and Fountains
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
I have concluded that if an electric sign is in the fountain, it must be at least 5 feet from the outside edge of the fountain and if it is permanently installed outside the fountain it can be right next ro the edge of the fountain and no special wiring methods apply. If it is a portable sign outside the fountain it must be located at least 5 feet from the edge of the fountain and be GFCI protected.

[This message has been edited by George Little (edited 11-21-2004).]

[This message has been edited by George Little (edited 11-21-2004).]

[This message has been edited by George Little (edited 11-21-2004).]
_________________________
George Little
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals