#90344 - 11/16/04 08:21 AM circuit for Tuff Shed
royta Offline
Member
Registered: 09/03/04
Posts: 138
Loc: CA
A homeowner would like me to install a fluorescent light fixture and a couple 120V receptacles in his new wooden Tuff Shed. He already has an existing Tuff Shed, which somebody previously installed a couple receps into, and he (homeowner) would like me to get the power for the second shed from the first shed.

There is at least one violation with the first shed, which is easily resolved; there is no disconnect at the shed. However, there is a second situation which I don't know is okay or not. Power to the first shed is obtained from an outside recep on the house. A weather proof extension box was installed, and PVC conduit run to the first shed. Does the first shed need it's own circuit from the panel, or is it okay to share another circuit from the house? If it needs it's own circuit, can the second shed use the same circuit as the first shed, or does each shed need their own circuit from the main panel?

I apologize if this seems simple to others, but I've actually never ran power to a remote building, where I didn't install a sub panel. I do however know that I will not need grounding electrodes at each shed, as per the Exception to 250.32(A).

[This message has been edited by royta (edited 11-16-2004).]
Top
2017 / 2014 NEC & Related Books and Study Guides
#90345 - 11/16/04 10:01 AM Re: circuit for Tuff Shed
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't see anything that prevents building 3 from being fed from building 2.
_________________________
Greg Fretwell
Top
#90346 - 11/16/04 10:29 AM Re: circuit for Tuff Shed
royta Offline
Member
Registered: 09/03/04
Posts: 138
Loc: CA
What about how building 2 (first shed) was fed in the first place?
Top
#90347 - 11/16/04 02:21 PM Re: circuit for Tuff Shed
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I don't know why you couldn't feed a shed from the outside receptacle, assuming that was legal (proper wiring, depth, GFCI and not off the bathroom).
At a certain point we may have some design issues but I don't see the code problem yet.
_________________________
Greg Fretwell
Top
#90348 - 11/16/04 02:30 PM Re: circuit for Tuff Shed
royta Offline
Member
Registered: 09/03/04
Posts: 138
Loc: CA
You are correct with the design issues. I'm looking forward to moving away from residential remodel work. Homeowner's only understand one thing, price. They don't care what it looks like as long as it's inexpensive. That doesn't do well for me, because I end up priding myself out of a job, or losing the job to a non-compliant bid. I might not know the code like I wish I did, but I will certainly find out what is right and wrong before starting an installation.

There actually is a code issue, but it will go away once I extend the circuit to the 2nd shed. The PVC conduit terminates into a handy box mounted on the outside of the shed. At least there is a weather proof cover on the handy box though.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals