#90273 - 11/11/04 09:57 AM Codes!!
rknikko Offline
Member
Registered: 02/02/04
Posts: 41
Loc: NY
1)What is the maximum length can be exposed for BX and Romex wires?
2)The code specify a need for receptacle within 25ft of a Heating or Cooling unit. What if the unit is outside of the house and the receptacle is inside of the house, but it's still within 25ft? Would that be OK?
Top
2017 / 2014 NEC & Related Books and Study Guides
#90274 - 11/11/04 11:43 AM Re: Codes!!
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
My answer to Q. 1 There is no limit to the length of exposed "Romex" cable or "BX" but there may be some issue with environment or physical protection. 334.15 for NM (Romex) and 320.15 for Armored Cable (BX) Q. #2- 210.63 is silent about the indoor or outdoor issue. It only says that it must be accessible and on the same level as the A/C unit.
_________________________
George Little
Top
#90275 - 11/11/04 01:47 PM Re: Codes!!
rknikko Offline
Member
Registered: 02/02/04
Posts: 41
Loc: NY
The BX cannot be exposed for more than 3ft I believe. When I say expose, I mean it will not be hidden in the wall. As for the attic, I believe this rule do not apply, but for finish wall, this is another case.
Top
#90276 - 11/11/04 02:13 PM Re: Codes!!
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
Don't know where you are getting the idea the BX, which is type AC now, cannot be run exposed. You can run it as long as you want subject to 320.15.

As to your question about the service receptacle, the code only says that it must be within 25 feet. I would not consider a receptacle in another space or inside the house to meet that requirement however.

-Hal
_________________________
www.myphonetechs.com
Top
#90277 - 11/11/04 04:36 PM Re: Codes!!
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
I don't think that a service receptacle inside for equipment outside would be in compliance with this part of the rule.
Quote:
The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment.

In most buildings the inside floor is at a higher level than the outside grade.
Don
_________________________
Don(resqcapt19)
Top
#90278 - 11/11/04 05:19 PM Re: Codes!!
hbiss Offline
Member
Registered: 12/16/03
Posts: 886
Loc: Hawthorne, NY USA
In most buildings the inside floor is at a higher level than the outside grade.

Well that may be stretching it a bit but I think the intent is to have the receptacle available for easy access by a serviceman and that's why the code requires one to be installed. If you had to run an extension cord through doors or windows we would be back to the days when the receptacle wasn't required.

-Hal
_________________________
www.myphonetechs.com
Top
#90279 - 11/11/04 05:53 PM Re: Codes!!
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
1) Many local town are adopting "exposed run" restriction, but that's a local Code issue, not one found in the NEC, as long as support requirements are met. My town started that a few years ago, limiting exposed runs of AC, MC & Greenfield to 24" from penetrations (except for motor and lighting whips). Most of the IL Lake Shore has already outlawed NM, so that's moot for us.

2) I've always installed one within L.O.S. of the HVAC in the basement - usually a lot less than 25'.

I've always heard the "25'" rule applied to roof mounted HVAC / mechanical stuff - so they wouldn't have to run extension cords from inside the building. (or to sign receptacles with adaptors)
Top
#90280 - 11/11/04 09:42 PM Re: Codes!!
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
What if the HVAC guy doesn't have access to the interior?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#90281 - 11/12/04 04:44 AM Re: Codes!!
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
I would always place the outlet in line of sight or next to the equipment.

I think it was in the code update notes that they were trying to prevent A/C guys from taking a leg of the A/C power and hooking up to the ground to provide power for their cords.
Top
#90282 - 11/12/04 09:34 PM Re: Codes!!
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
 
Aside — There are odd little special-application fused-receptacle/disconnect switches like that at: www.midwestelectric.com/marketing/literature/MEPF-AC04.pdf
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals