The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 102 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#90254 - 11/10/04 06:12 PM IT room grounding
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
 Quote:
645.15 Grounding.
All exposed non–current-carrying metal parts of an information technology system shall be grounded in accordance with Article 250 or shall be double insulated.


How in this context, would one interpet this code for size requirement, and point of connection? i.e. To nearest equipment ground, MPOE (TelCo), Main service, and what size?

BTW this is for Ladder rack and and Equipment rack grounding, served by 70A UPS

Any comments would be helpful

TANKS Mark
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
2014 / 2011 NEC & Related Books and Study Guides
#90255 - 11/10/04 06:36 PM Re: IT room grounding
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Mark:
IMHO, you cannot go wrong with installing a bond jumper (rated at 70 amp) from rack to ladder frame, and to bldg steel, or h2o piping.

Another 'gray' area???

John
_________________________
John

Top
#90256 - 11/10/04 10:50 PM Re: IT room grounding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I agree with John. The general rule on grounding and bonding is you size the grounding conductor based on the circuit that is likely to energize the protected equipment. In your case I would say it was the 70a UPS and 250.122 says that is a #8 copper or #6 al. This should be bonded to the EGC of the UPS supply conductors or back to the panel grounding bus, in my opinion.
I suppose you could go to building steel if you can assure that it is effectively bonded back to the grounding system but a water pipe is not usually an acceptable ground these days. Too much plastic in the plumber's trade.

[This message has been edited by gfretwell (edited 11-11-2004).]
_________________________
Greg Fretwell

Top
#90257 - 11/10/04 11:18 PM Re: IT room grounding
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
OK the reason I asked....

LV sub doing the install of the ladder rack asked for 1/0 AWG???? To the main!!!!

An engineering note mentions 4/0! No location specified.

Now some other info that I left out, this is an it room covering an tenent buildout area fed by two 200A panels.

I can be one to follow spec's, but when I get conflicting ones I get itchy. Then again, I like to know why things are they way they ask. I have put these in several different ways now, as spec's dictate.

So what dictates the size of this ground, and where it comes from. Personally I think a #6 equipment ground would be fine, or for that matter to the MPOE ground.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#90258 - 11/11/04 04:27 AM Re: IT room grounding
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
There is lots of flexibility in the size (as long as you exceed the minimum) and exactly where it terminates as permitted by Article 250.
The Engineer may have a reason he/she wants 4/0AWG, don't reduce it without a nice credit
_________________________
Ron

Top
#90259 - 11/11/04 09:53 AM Re: IT room grounding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If this guy is going for reducing transients on the ladder rack I can see wanting to go back to the grounding electrode (star wired ground system) but I think the wire size may be excessive. These days noise rejection is a lot better in IT equipment than it was in the 70s but a lot of people have not adjusted their thinking.
There is more urban legend in IT than any other industry I can think of. A lot of these grounding practices have simply taken on a life of their own and no amount of logic will get people to budge.
_________________________
Greg Fretwell

Top
#90260 - 11/11/04 12:59 PM Re: IT room grounding
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
 
One origin of giant grounding conductors is the telecomm biz.

At least the blind-copycat boilerplate does not call for 4/0AWG seven-strand or does it? Another good one is exothermic welds to aluminum {or fiber-glass!} cable tray.

Two general references for power—signal ground ‘interfacing’ are IEEE emerald book described at http://shop.ieee.org/ieeestore/Product.aspx?product_no=SS94741 and the parchment scrolls of FIPS PUB 94 www.itl.nist.gov/fipspubs/fip94.pdf




[This message has been edited by Bjarney (edited 11-11-2004).]

Top
#90261 - 11/12/04 08:42 PM Re: IT room grounding
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
In the "old days", there was a lot of RS-232 and similar stuff running around. RS-232 connections are direct electrical connections between the equipment, using the equipment ground as a voltage reference. A small difference in the ground voltage can kill equipment like this, and it doesn't take much noise in the grounding system to cause data errors.

More recent stuff, like Ethernet, uses differential, transformer-isolated connections. These transformers are rated to withstand a 2,000 volt potential difference between the communication line and the equipment. Because the connection is differential, it has something like a 60-90 dB rejection of common-mode voltage. It's really hard for a grounding problem to cause a problem in the equipment. And even if really severe noise on the grounds causes occasional data errors, most modern communication protocols have error detection and recovery mechanisms built in, so errors normally just result in a minor degradation in throughput.

Interesting historical note: When Xerox installed their first prototype Ethernet network, they found that there was something like a 90V difference in ground potential from one end of the building to the other! That affected our thinking about isolation, so when we designed the 10 megabit Ethernet standard, we made sure that everything was transformer isolated.


[This message has been edited by SolarPowered (edited 11-12-2004).]

Top
#90262 - 11/13/04 08:29 PM Re: IT room grounding
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I guess you never worked in Florida ;-)

I agree these LANs will do pretty well with huge DC and 60hz ground shifts but when you get short rise time transients like you see with nearby lightning strikes the only way to fix it is with copper. If we ran between different buildings or services with separate grounding systems we bonded them together. In some cases we even bonded individual machines together.
These are really those dreaded "ground loops" but as you say, these things reject that noise on the data side. This is actually a power hit that fries transistors. It may just be a regional thing tho. I don't remember this kind of thing happening much in Md
_________________________
Greg Fretwell

Top
#90263 - 11/14/04 08:16 PM Re: IT room grounding
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Hey, we have lightning storms here, too! I think I remember one sometime in the last three or four years.

Top