An owner of a single family home wants to install wind turbines and solar panels on his roof.

In a nutshell--What would you ask for as the plan reviewer who has to review the electrical portion of the job (not structural support)?

I have come up with:
1)A complete one-line diagram showing all associated equipment.

2)Show the location of all the equipment.

3)Provide Manuf. specs on all equipment.

4)Provide the rating of all OCPD's.

5)Provide dc system voltage of PV output circuit and combined turbine and PV output circuit.

6)Provide a letter from the utility giving their approval of the system.
Top
2017 / 2014 NEC & Related Books and Study Guides
#90246 - 11/09/04 08:47 AM Re: Hybrid System
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Bonding?
_________________________
Greg Fretwell
Top
#90247 - 11/09/04 03:36 PM Re: Hybrid System
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
 
In some areas, typical electrical-standards boilerplate for small PV/inverter installations is IEEE 929, UL 1741 and NEC 690.
Top
#90248 - 11/09/04 06:04 PM Re: Hybrid System
John Steinke Offline
Member
Registered: 04/03/01
Posts: 518
Loc: Reno,Nv., USA
Don't forget a "ladder logic" diagram showing how this mess will be controlled.
Top
#90249 - 11/10/04 06:44 PM Re: Hybrid System
HotLine1 Online   content


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
OK< sunlight resistant cables, wiring, suitable bushings, connectors, raceways, etc.
Sunlight resistant ty-wraps, discos (utility requirement here)

The other AHJ is the solar cell maven, I'll see if he has a op to stop over here next week

John
_________________________
John
Top
#90250 - 11/10/04 06:54 PM Re: Hybrid System
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
If these Wind Turbines, Solar panels, and associated wiring don't comply, what would an inspector do? AS far as the power they produce, there would be no meter to pull or hold hostage.

Roger
Top
#90251 - 11/11/04 05:14 PM Re: Hybrid System
WireWrestler Offline
Member
Registered: 10/29/01
Posts: 45
Loc: Northern IL
We install the same type of systems you are talking about. I assume you are on the ComEd grid. If the systems are to be grid-tied for net metering they must meet the UL1741 spec. mentioned. As far as I know, all of the off the shelf equipment does. I recomend that you go to http://www.bergey.com/ They have the most information and best wind turbines available. We are dealers for them and they are great.
Bob
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals