The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
1 registered (HotLine1), 165 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#90222 - 11/02/04 10:01 PM Plastic boxes/Commercial use
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Are plastic boxes ok to use in commercial buildings? Some do have a knockout for pipe or mc cable to run into.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
2017 / 2014 NEC & Related Books and Study Guides
#90223 - 11/03/04 10:05 AM Re: Plastic boxes/Commercial use
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Non-metallic boxes cannot be used with metallic wiring methods unless meeting one of the two exceptions. 314.3.
_________________________
John

Top
#90224 - 11/03/04 08:12 PM Re: Plastic boxes/Commercial use
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
Why then is there a 1/2" knockout? for PVC? What would be wrong with plastic boxes, there used in homes?
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#90225 - 11/03/04 10:09 PM Re: Plastic boxes/Commercial use
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
The non-metalic boxes with standard K.O’s are for ENT (smurf tube) or can be used with RNMC. There is nothing wrong with non-metallic boxes when used with non-metallic wiring methods. You can’t use metal raceways or cable armors with non-metallic boxes since the raceway or armor would not be properly bonded.

Curt
_________________________
Curt Swartz

Top
#90226 - 11/04/04 08:17 AM Re: Plastic boxes/Commercial use
aldav53 Offline
Member

Registered: 08/22/01
Posts: 547
Loc: Chandler, AZ USA
caselec,
Yes true, unless you run metal cable from a bonded metel panel to the plastic box, then its bonded at one end.
_________________________
The Golden Rule - "The man with the gold makes the rule"

Top
#90227 - 11/04/04 12:52 PM Re: Plastic boxes/Commercial use
zapped208 Offline
Member

Registered: 02/18/03
Posts: 201
Loc: Somewhere in USA
electricman2 has the correct response.
I wonder if a twin M/C connector would satisfy the exception to 314.3?
_________________________
Shoot first, apologize later.....maybe

Top