#90198 - 11/02/04 05:10 PM Derating Application
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
We had one of our crews run into a situation yesterday with derating.

Final inspection, a new office in a converted industrial space. The guys had run 7 ckts. in a 3/4" emt. 7 hots, 7 neutrals, one ground, #12 thhn, 20a ocpd.

The state inspector failed them for derating. He said that, "Since this was a single phase service all neutrals are counted as current carrying conductors." These circuits are all general use plugs and lighting. No Non-linear loads, no HID lighting.

My repsonse is WTF??????? This is definitely a new one on me. I consider that conduit to have 7 current carrying conductors per the NEC. Please educate me if I'm wrong.

GJ
Top
2017 / 2014 NEC & Related Books and Study Guides
#90199 - 11/02/04 05:16 PM Re: Derating Application
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I don't know how other guys figure this, but I'm pretty sure if I took the neutral out of the service and pinched it's end between my fingers, then, with a different finger, touched the screw where it came from I'd find it to be "current-carrying", so I count it as such.

(Don't try this at home.)

Dave

[This message has been edited by Dave55 (edited 11-02-2004).]
Top
#90200 - 11/02/04 06:39 PM Re: Derating Application
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
Current may indeed flow through your fingers but I dare say it would be "unbalanced current" and thus 310.15(B)(4)(a)would apply, no?

310.15(B)(4)(a)
A neutral conductor that carries only the unbalanced current from other conductors of the same circuit shall not be required to be counted when applying the provisions
of 310.15(B)(2)(a). (derating table)
Top
#90201 - 11/02/04 06:48 PM Re: Derating Application
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I understand that portion of the NEC to apply to multiwire branch circuits. As it is described as 7 hots and 7 neutrals for 7 circuits, I don't think it applies.

Dave
Top
#90202 - 11/02/04 06:56 PM Re: Derating Application
Norstarr Offline
Member
Registered: 09/25/04
Posts: 86
Loc: Wi
Junkie,
I'm under the impression that you have 7 two wire circuits which means they are all current carrying conductors. Looking at 310.15(B)(2)(a) you find that you must derate to 50% of the thhn value of 30A and the ocpd would be 15A.
Why aren't you installing 3 wire circuits which would reqire you to derate to 70% and your ocpd would be 20A?
Ron
Top
#90203 - 11/02/04 07:19 PM Re: Derating Application
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
You guys are right. I was thinking 3 wire circuits with shared neutral. Separate neutral with each phase wire - all neutrals are indeed current carrying conductors.
Top
#90204 - 11/02/04 07:21 PM Re: Derating Application
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Nailed on derating, and fill factor.

358.22 to Chapter 9 Table 1, and notes to Tables. 40% fill, not 88%.

The only way I could see 15 #12's being allowed, is if were in a 23" conduit, and even then, I wouldn't do it.



[This message has been edited by e57 (edited 11-02-2004).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#90205 - 11/02/04 07:36 PM Re: Derating Application
Dave55 Offline
Member
Registered: 05/08/04
Posts: 697
Loc: Crystal Lake, Illinois, USA
I use Annex C, Table C1 Maximum Number of Conductors....in EMT.

Type THHN, THWN for 3/4" EMT is 16 conductors for 12 ga. Of course there would be some derating involved.

Dave
Top
#90206 - 11/02/04 07:42 PM Re: Derating Application
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
Up to 16 THHN conductors in 3/4" EMT allowed per table C1 in annex C.
Top
#90207 - 11/02/04 08:06 PM Re: Derating Application
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
Mark,
The tables in Annex C are not 100% fill, they are based on Chapter 9 Table 1. (16) #12 THHN conductors would meet the 40% fill requirement for ¾” EMT according to Annex C Table C1.
The area of #12 THHN is .0133”
16 X .0133 = .2128”
¾” EMT is .213 @ 40% fill

Curt
_________________________
Curt Swartz
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 74 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals