The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tjia1981), 219 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89991 - 10/26/04 08:08 PM UF Cable Under Pool Apron
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Any restrictions on installing UF cable under a pool apron? Not under the pool itself.

Looking at running switch legs under 6 inch apron around pool.

Feeder from sub panel on side of house will be in PVC...insulated ground and neutral..#8 from pool steel and it is insulated...did see that the pool guy just wrapped the wire under a nut on a 3/8 stud..that did not look too good but i am not doing that part..just tieing in the ground from the pool steel to the egc from the sub..any prob with that?

i thought i read somewhere that any runs under a pool had to be in conduit..my memory aint what it used to be..

thanks for any replies...

-regards

Mustang
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#89992 - 10/26/04 08:27 PM Re: UF Cable Under Pool Apron
John Steinke Offline
Member

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
I can't speak for the code, but...

I advise against it, because I currently have a customer whose pool apron covers a bad wire run. Since UF was used, replacing this wire is almost impossible to replace this wire, without tearing up the apron.
Also, im my experience, trenches are NEVER deep enough, and UF is almost always run way too shallow.
Run pipe, then transition in a ground box once past the apron area.

Top
#89993 - 10/26/04 08:28 PM Re: UF Cable Under Pool Apron
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Mustang,
Where do these switchlegs go??

AFAIK there is nothing that would keep you from putting UF under a pool deck. However, I don't think I'd go that route unless there was no other option. It definitely would be better to go with pvc conduit.

Top
#89994 - 10/26/04 08:37 PM Re: UF Cable Under Pool Apron
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Thanks for the reply. I think you are right and I will go ahead and do this whole job in pvc.

the switches will be controlling the wet niche lighting and 4 coach lights fed from a gfi..

i can easily justify the cost difference..

thanks for taking the time to reply..

-regards

mustang
_________________________
Electricity has no respect for ignorance!

Top
#89995 - 10/26/04 10:57 PM Re: UF Cable Under Pool Apron
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You are also supposed to be 5' from the pool if space is available 680.10
_________________________
Greg Fretwell

Top