#89971 - 10/26/04 06:48 AM Using a sub feed lug
Norstarr Offline
Member
Registered: 09/25/04
Posts: 89
Loc: Wi
Have a 100 amp main breaker panel in a residence. Have to add a sub panel and plan to feed it with #4's and use a sub feed lug instead of a breaker. The sub panel is then protected by the 100 amp main breaker. Any code violation here?
Ron
Top
2017 / 2014 NEC & Related Books and Study Guides
#89972 - 10/26/04 07:30 AM Re: Using a sub feed lug
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
I would double check the stab ratings on the main panel that is feeding the sub. Some panels limit the maximum current ratings of loads connected to a single bus stab.

Also the use of #4s falls right onto an ugly bit of NEC 310.15(B)(6). #4Cu is permitted to be protected with a 100A OCPD when it is used to supply the _main_ power feed of a single residence. #4Cu does not have sufficient ampacity to be protected at 100A _in general_, but for the specific load described in 310.15(B)(6) it is permitted to do so. This means that #4Cu is _not_ sufficient for the feed to a 100A subpanel.

But there is yet another exception, which is that the feed to any subpanel in a residence is not required to be larger than the main feed. So I think that using the #4Cu as you describe will be okay until such time as the main service is upgraded, at which point you will need to protect the subpanel at less than 100A.

-Jon
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
2 registered (dougwells, Admin), 190 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals