The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/22/16 09:52 PM
International Wire Colour Codes
by Texas_Ranger
10/22/16 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89939 - 10/24/04 08:14 PM 2 wire terminal?
bp-redbear Offline

Registered: 08/30/04
Posts: 53
Loc: NY
I believed that the "only one conductor per terminal" rule was all-encompassing, but in reading 110.14(A) Terminals (2002NEC), it mentions "Terminals for more than one conductor...shall be so identified".

One of my co-workers says that when wiring in a main panel, he terminates the grounded conductor and the grounding conductor of the same circuit under the same screw on the terminal bus, if there are no separate GND and NEUT bars.

Is he complying with the NEC in diong this?

Are terminal bars in breaker panels "identified" or rated (listed) for two conductors under each terminal (screw)?

Started doing this myself, but, not sure of the integrity of both wires having same pressure, and remaining securely attached.

2014 / 2011 NEC & Related Books and Study Guides
#89940 - 10/24/04 08:32 PM Re: 2 wire terminal?
Dave55 Offline

Registered: 05/08/04
Posts: 666
Loc: Crystal Lake, Illinois, USA
I rarely run Romex, but when I do I have put the neutral and ground under the same screw. I'm a little bleary-eyed to look it up now, but my feeling on the matter is that the neutral and ground are bonded at the service and the terminal is plenty large enough.

Where I see it that is definitely wrong is on the line side of the main breaker.

(edited for spelling)

[This message has been edited by Dave55 (edited 10-24-2004).]

#89941 - 10/24/04 08:39 PM Re: 2 wire terminal?
sparky806 Offline

Registered: 12/07/02
Posts: 59
Loc: Shawnee, KS, USA
408.21 tells me you can't do it.

Each grounded conductor shall terminate within the panalboard in an indivdual terminal that is not used for another conductor.

#89942 - 10/25/04 05:12 AM Re: 2 wire terminal?
George Little Offline

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
I agree with Sparky and would add that there are panels in use out there that are Listed and permit the "grounding" conductor to be terminated under the same screw with other "grounding" conductors and the combinations are clearly indicated in the spec sheet inside the panel. I know of no panels that allow the connection of the grounded and grounding conductor under the same screw.
George Little

#89943 - 10/25/04 06:34 PM Re: 2 wire terminal?
John Steinke Offline

Registered: 04/03/01
Posts: 509
Loc: Reno,Nv., USA
I agree that placing the bare and white wires under the same screw is a bad ides- even though it makes for a neater panel.
What you can do, however, is twist as many as three bare wires together, then place them under one screw.
Of course, it's not that hard, or expensive, to add a ground bar.

#89944 - 10/25/04 10:29 PM Re: 2 wire terminal?
Big Jim Offline

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
I've not seen a panel where the listing allows for more than 2 ground wires under 1 screw. # would be a violation of the listing in most cases.

#89945 - 10/26/04 10:18 AM Re: 2 wire terminal?
markp Offline

Registered: 04/12/04
Posts: 60
Loc: Kent, WA, USA
Look at the Cutler-Hammer CH series (and I think the BR series too). They can accomodate up to three #10-#14 grounding wires in a single hole. Must be the same type of wire in each hole.

CH breakers are also listed for 2 wires in each hole when small wires (#10 - #14 I believe) are used.

CH is great with providing all of the important listing information you need stamped on their breakers and panels.
Kent, WA

#89946 - 10/27/04 02:57 AM Re: 2 wire terminal?
Big Jim Offline

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
The rule is pretty simple. You can do what the listing allows. I think you would assume 1 wire per screw unless specifically listed for more.