The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#89916 - 10/24/04 12:18 PM Range hoods require an individual branch circuit
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Look at what is NEW in Article 422 for cord and plug connected Range Hoods!

.......

 Quote:
(5) The receptacle shall be supplied by an individual branch circuit.


[See ROP 17–21]

Why? What was the substantiation?
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#89917 - 10/24/04 12:26 PM Re: Range hoods require an individual branch circuit
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
That is a good question Joe.

Do you mind if I just guess at the substantiation?

Could it be that it is expected a microwave hood combo unit may be installed at some later date?

I hope I am wrong about that.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89918 - 10/24/04 12:39 PM Re: Range hoods require an individual branch circuit
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Not making light of the issue, but I must live a sheltered life in that I have never installed a cord and plug connected range hood.

Roger

Top
#89919 - 10/24/04 12:52 PM Re: Range hoods require an individual branch circuit
capt al Offline
Member

Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Roger, guess I have lived the same way. Never installed one in the 25 years I've been doing electrical work. Every range hood I have connected was hard wired.

Al

Top
#89920 - 10/24/04 01:00 PM Re: Range hoods require an individual branch circuit
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Hello Al, whew, I'm glad I'm not alone here.

Roger

Top
#89921 - 10/24/04 01:04 PM Re: Range hoods require an individual branch circuit
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Roger and Al where did you locate the disconnect switch?

Not in the cabinet I hope, that would be a 110.26 violation.

Just kidding I have only seen hard wired hoods also.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89922 - 10/24/04 03:28 PM Re: Range hoods require an individual branch circuit
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
One reason you guys may not have seen a cord connected range hood is that they are sold at the Big Box stores and usually not installed by 'electricians'.

422.16(B)(4)Range Hoods.
Range hoods shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the use on range hoods in the installation instructions of the appliance manufacturer, where all of the following conditions are met:


Bob, your reasoning is right on the money! See page 206 of the 2005 Analysis book.


Substantiation:
Many times range hoods are removed and replaced with a "microwave type" range hood. Allowing cord and plug connection will make the installation much easier for the homeowner because no "electrical change" to the wiring system will be required.

Panel Statement:
The permission to use cord-and-plug connection provides the ability to upgrade to a combined microwave range hood. The panel added the additional requirements to ensure a safe installation of a combined microwave range hood.


***This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field.****

Pierre
_________________________
Pierre Belarge

Top
#89923 - 10/24/04 03:37 PM Re: Range hoods require an individual branch circuit
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I agree Pierre. It sure seems strange that this passed. How many proposals do you see that really are good ideas but have no technical substantiation and get shot down because of it? It seems to me that this is no diffferent than the rest of them.
_________________________
Ryan Jackson,
Salt Lake City

Top
#89924 - 10/24/04 03:51 PM Re: Range hoods require an individual branch circuit
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Pierre

 Quote:
This statement and code change says something to me that makes me very uneasy. Why is the NEC making code changes based on Homeowners performing installations. ELECTRICIANS should be installing electrical work and using the NEC as well as their learned skills from the field


Well said.

I also think of this.

 Quote:
This Code contains provisions that are considered necessary for safety. Compliance therewith and proper maintenance will result in an installation that is essentially free from hazard but not necessarily efficient, convenient, or adequate for good service or future expansion of electrical use.


With this reasoning 30 and 50 amp outlets should be provided at gas dryers and ranges in case the homeowner decides to change to electric in the future.

We better run 10/3 to this hood outlet in case the microwave hood combo that might be installed has browning elements.

Well I can't complain as I was not involved in the code making process.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89925 - 10/24/04 04:54 PM Re: Range hoods require an individual branch circuit
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
I have been giving residential hoods thier own circuit for years. Most of the higher end ones really suck if you know what I mean, multiple motors, lighting, heat lamps, etc. Some will pull upwards of 12A. Justification alone for a dedicated circuit. However, I haven't seen one cord connected yet either??? Where would one place a plug for such an animale?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top