The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 248 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89878 - 10/22/04 11:07 AM Generator Wiring
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Any tips on connecting a 400A Generator for temporary power?

I appreciate any replies.

-regards

Mustang
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#89879 - 10/26/04 03:44 PM Re: Generator Wiring
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
If the set up will be temporary I would tie the generator into the Service Disconnecting means load side wiring if possible. This presumes that the generator has a main breaker that will serve in place of the Service Disconnecting Means. It also presumes that the service disconnecting means is a separate piece of equipment that is connected to the load by field installed wiring.

If, on the other hand, the service equipment is some sort of combined main breaker and panel equipment then you will need to use a double block and break technique to isolate the building from the utility power. If the building is supplied through a 400 ampere meter socket than you would open the service disconnect, pull the meter, blank off the meter socket and disconnect the meter load wiring from the service disconnecting means. You would then blind off the meter load wiring with insulating materials. That makes the line side terminals of the service disconnecting means available for connecting the generator to. Since meter sockets in the four hundred ampere size are often equipped with shunts you will have to secure the shunt in the open position. The same lever is often used to release the meter jaws and engage the shunt bypass. These have to be operated to the open position after having removed the meter. If the service is larger than four hundred amperes then removing the meter will not deenergize the service disconnecting means line side terminals. So check for voltage every step of the way.
--
Tom H
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#89880 - 10/26/04 05:14 PM Re: Generator Wiring
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Thanks for the reply. You were right when you said it is a temporary one and the gen set has it's own OCPD and it also has a multi tap transformer to give several different voltage configurations.

We will tie the feeder from the gen set ocpd to a gutter that feeds several exisitng MB panels. we will use the existing ground rod to ground the system.

I am assuming no other path to ground is allow so as not to create a difference of potential on the gen set xfmr?

i have seen portable welders that if not grounded properly can be very dangerous.

no need to ground to building steel if the building is bonded through the first disconnect/panel to the gec?

thanks for the replies..

-regards

greg