ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,665 Are you busy
166,575 Re: Forum
160,753 Need opinion
Who's Online Now
2 registered members (gfretwell, SteveFehr), 62 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#89878 - 10/22/04 02:07 PM Generator Wiring  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Any tips on connecting a 400A Generator for temporary power?

I appreciate any replies.

-regards

Mustang


Electricity has no respect for ignorance!

2017 / 2014 NEC & Related Books and Study Guides

#89879 - 10/26/04 06:44 PM Re: Generator Wiring  
tdhorne  Offline
Member
Joined: Mar 2001
Posts: 345
Maryland, USA
If the set up will be temporary I would tie the generator into the Service Disconnecting means load side wiring if possible. This presumes that the generator has a main breaker that will serve in place of the Service Disconnecting Means. It also presumes that the service disconnecting means is a separate piece of equipment that is connected to the load by field installed wiring.

If, on the other hand, the service equipment is some sort of combined main breaker and panel equipment then you will need to use a double block and break technique to isolate the building from the utility power. If the building is supplied through a 400 ampere meter socket than you would open the service disconnect, pull the meter, blank off the meter socket and disconnect the meter load wiring from the service disconnecting means. You would then blind off the meter load wiring with insulating materials. That makes the line side terminals of the service disconnecting means available for connecting the generator to. Since meter sockets in the four hundred ampere size are often equipped with shunts you will have to secure the shunt in the open position. The same lever is often used to release the meter jaws and engage the shunt bypass. These have to be operated to the open position after having removed the meter. If the service is larger than four hundred amperes then removing the meter will not deenergize the service disconnecting means line side terminals. So check for voltage every step of the way.
--
Tom H


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

#89880 - 10/26/04 08:14 PM Re: Generator Wiring  
mustangelectric  Offline
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
Thanks for the reply. You were right when you said it is a temporary one and the gen set has it's own OCPD and it also has a multi tap transformer to give several different voltage configurations.

We will tie the feeder from the gen set ocpd to a gutter that feeds several exisitng MB panels. we will use the existing ground rod to ground the system.

I am assuming no other path to ground is allow so as not to create a difference of potential on the gen set xfmr?

i have seen portable welders that if not grounded properly can be very dangerous.

no need to ground to building steel if the building is bonded through the first disconnect/panel to the gec?

thanks for the replies..

-regards

greg


Electricity has no respect for ignorance!


Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 208
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.7509 MB (Peak: 0.8749 MB) Zlib enabled. Server Time: 2017-03-29 01:25:42 UTC