The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 216 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#89780 - 10/19/04 01:02 PM Sizing Neutral
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
When sizing a neutral on commercial applications, can 70% be taken? I have a 100 amp. single phase sub panel fed by # 3 copper. What size neutral can I use? I tried to find it in the code, but can't seem to locate it. Can't seem to keep up with it all. Where can I find it in the code? I usually just run the same as phase conductors, but I may need to downsize if I can, to use a smaller pipe size. Thanks a lot. Steve

Top
2014 / 2011 NEC & Related Books and Study Guides
#89781 - 10/19/04 01:25 PM Re: Sizing Neutral
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Try 2002 N.E.C. 220.22

Top
#89782 - 10/21/04 05:15 PM Re: Sizing Neutral
tdhorne Offline
Member

Registered: 03/22/01
Posts: 344
Loc: Maryland, USA
 Quote:
When sizing a neutral on commercial applications, can 70% be taken? I have a 100 amp. single phase sub panel fed by # 3 copper. What size neutral can I use? I tried to find it in the code, but can't seem to locate it. Can't seem to keep up with it all. Where can I find it in the code? I usually just run the same as phase conductors, but I may need to downsize if I can, to use a smaller pipe size. Thanks a lot. Steve


Is this sub panel supplied from a single phase service or is it supplied from a three phase service. If the feeder is from a three phase service than the grounded current carrying conductor will carry just as much current as the phase conductors.
--
Tom Horne
_________________________
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison

Top
#89783 - 10/21/04 08:57 PM Re: Sizing Neutral
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
We need to know the load and type of supply to determine if you can reduce the grounded conductor. Some panels you can reduce the grounded conductor on three phase or single phase.
_________________________
George Little

Top
#89784 - 10/22/04 05:05 AM Re: Sizing Neutral
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
The way I read it There can be no reduction in the Feeders & Service Neutrals till over 200 amps. Then after that 70% of the unbalanced load over 200amps, IF it meets the previsons of that section.And No reduction in some cases depending on type of service and type of loads.Such as an unbalanced Wye System.Some cases the Neutral Should be upsized.

Top
#89785 - 10/22/04 05:10 AM Re: Sizing Neutral
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Also look at 250.24b1 for additional info on ungrounded conductor sizes.

Top
#89786 - 10/22/04 07:22 AM Re: Sizing Neutral
sparkync Offline
Member

Registered: 10/17/02
Posts: 811
Loc: NC
The sub panel is fed from a single phase service. The load at this point will very little, about 30 or 40 amps, but I am supplying additional spaces for future expansion. It is a business which may add more equipment. I'm thinking I will go ahead and pull the same size neutral anyway to be safe. Thanks Steve

Top
#89787 - 10/22/04 07:47 AM Re: Sizing Neutral
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Yoopersup,
 Quote:
There can be no reduction in the Feeders & Service Neutrals till over 200 amps.

Are you saying for feeders less than 200 amps the neutral must be the same size as the ungrounded conductors?
Don
_________________________
Don(resqcapt19)

Top
#89788 - 10/22/04 08:05 AM Re: Sizing Neutral
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Don
(Under cetain conditions) Yes, And sometime the Netural Should be larger then the ungrounded conductors.

Top
#89789 - 10/22/04 10:28 AM Re: Sizing Neutral
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Yoopersup,
Then I don't agree with your statement. 220.20 only requires that the grounded conductor of a feeder be sized to the maximum unbalanced load. If this maximum unbalanced load exceeds 200 amps, then you only need to size the grounded conductor for 200 amps plus 70% of the unbalanced load greater than 200 amps. If you have a 120/240 volt panel where there is a one 20 amp single pole breaker and ten 2 pole 40 amp breakers for 240 volt loads, the ungrounded conductor could be 500 kcmil and the grounded conductor #12 and be compliant with the rules in the NEC.
Don
_________________________
Don(resqcapt19)

Top