The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (hyetal), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89778 - 10/19/04 06:44 AM 125% and 60deg.
cgw Offline

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Please correct me if I am wrong.
1. For electric heat, the branch circuit size needs to be based on 125% of the full load amps.
2. Conductors (under 100A) need to be selected at 60degC unless the terminations are rated for 75degC.

2014 / 2011 NEC & Related Books and Study Guides
#89779 - 10/19/04 09:27 AM Re: 125% and 60deg.
gfretwell Offline


Registered: 07/20/04
Posts: 9023
Loc: Estero,Fl,usa
Sounds right to me but I would look closely at the terminations. Most, over 30a are 75c from what I have seen. Of course YMMV so you have to look.
Of course if you are using Romex you are stuck with 60c anyway.
Greg Fretwell