#89778 - 10/19/04 06:44 AM 125% and 60deg.
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Please correct me if I am wrong.
1. For electric heat, the branch circuit size needs to be based on 125% of the full load amps.
2. Conductors (under 100A) need to be selected at 60degC unless the terminations are rated for 75degC.
Top
2017 / 2014 NEC & Related Books and Study Guides
#89779 - 10/19/04 09:27 AM Re: 125% and 60deg.
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Sounds right to me but I would look closely at the terminations. Most, over 30a are 75c from what I have seen. Of course YMMV so you have to look.
Of course if you are using Romex you are stuck with 60c anyway.
_________________________
Greg Fretwell
Top