The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 03:29 PM
Looking for older post
by Texas_Ranger
Today at 03:22 PM
Safety at heights?
by gfretwell
Today at 02:19 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
0 registered (), 79 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#89778 - 10/19/04 06:44 AM 125% and 60deg.
cgw Offline
Member

Registered: 07/29/04
Posts: 133
Loc: Rochester NY
Please correct me if I am wrong.
1. For electric heat, the branch circuit size needs to be based on 125% of the full load amps.
2. Conductors (under 100A) need to be selected at 60degC unless the terminations are rated for 75degC.

Top
2017 / 2014 NEC & Related Books and Study Guides
#89779 - 10/19/04 09:27 AM Re: 125% and 60deg.
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Sounds right to me but I would look closely at the terminations. Most, over 30a are 75c from what I have seen. Of course YMMV so you have to look.
Of course if you are using Romex you are stuck with 60c anyway.