#89742 - 10/17/04 09:45 AM Ground Rod
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
What are the required dimensions for a galvanized steel rod if it is to be used as a gounding electrode? Trick question.
_________________________
George Little
Top
2017 / 2014 NEC & Related Books and Study Guides
#89743 - 10/17/04 09:50 AM Re: Ground Rod
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I will take a swing at this.

5/8" x 8' minimum.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89744 - 10/17/04 09:55 AM Re: Ground Rod
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Ah the new Galvan Electric rod huh?

If U/L is OK with it I am OK with it ... until someone tells me otherwise.
_________________________
Greg Fretwell
Top
#89745 - 10/17/04 10:13 AM Re: Ground Rod
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I agree with Bob.
_________________________
Ryan Jackson,
Salt Lake City
Top
#89746 - 10/17/04 10:13 AM Re: Ground Rod
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Wouldn't we have to wait for 250.52(A)(5)(b) to get changed?

Quote:
250.52(A)(5)(b)Electrodes of rods of iron or steel shall be at least 15.87 mm (5/8 in.) in diameter. Stainless steel rods less than 16 mm (5/8 in.) in diameter, nonferrous rods, or their equivalent shall be listed and shall not be less than 13 mm (1/2 in.) in diameter.


In my mind a galvanized steel rod is not equivalent to Stainless steel or nonferrous rods.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89747 - 10/17/04 10:29 AM Re: Ground Rod
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Boy, you guys are right on top of your game. Yes it is all about the Galvan Electric rod. 250.25(A)(5)(b) is kinda poorly written (surprise, surprise) and hopefully it will get re-written someday. In talking with NEMA rep. they use the word "nominal" meaning something in name only when talking about a 5/8 ground rod. Actual dimensions are considerably less than 5/8". The Galvan rod is also less than 5/8" but it has the blessing of UL and I am not sure but maybe we should lean towards using this listed product rather than using and approving the "nominal" 5/8" rod.
_________________________
George Little
Top
#89748 - 10/17/04 11:16 AM Re: Ground Rod
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
I remember the last time this rod was talked about, and the site like had a whole "justification" page about thier listing, and sizing.
http://www.galvanizersonline.com/electrical/faq.asp

George, do you have stock in this company? I don't get the reason why this would be better than a "regular rod"?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#89749 - 10/17/04 11:26 AM Re: Ground Rod
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
From their site.

Quote:
What does the NEC Code say about ground rod electrode diameters?

Diameters must be 0.625 inches minimum and the rod length must be 96 inches (8 feet) minimum. Any rod less than 0.625 inches DOES NOT meet the NEC Code, unless it is “listed.” Galvan has achieved this compliance!


What I don't understand is the compliance with "equivalent to Stainless steel or nonferrous rods."

Who decided a galvanized rod is equivalent and if it is what type of rod would not be equivalent?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89750 - 10/17/04 11:34 AM Re: Ground Rod
CharlieE Offline
Member
Registered: 04/23/04
Posts: 200
Loc: Indianapolis
This reminds me of the question, "What is the inside diameter of 1/2" conduit?"

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy
_________________________
Charlie Eldridge, Indianapolis Utility Power Guy
Top
#89751 - 10/17/04 12:36 PM Re: Ground Rod
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
To answer e57, I don't have stock in Galvan, wish I did. This question came up at one of our local inspector forums and got us all talking. I have invited the rep for Galvan to our IAEI Annual Michigan Chapter meeting in December and gave him a 15 minute part on the program to clear up the matter. Somehow I doubt 15 minutes will get it.
_________________________
George Little
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals