The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (ampherder), 184 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#89653 - 10/12/04 02:20 PM Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
Hi,
Is connecting the gec to building steel on a commercial job accpetable versus cold water bond?

it seems to me that you need both but parallel paths could be an issue.

i am looking at a riser diagram that calls for 3 3/4"X8' ground rods placed 10 feet apart and instructions to connect to building steel where possible..

it seems to me that you need a building steel connection and you need a cold water bond..200A service requires a #6 AWG GEC to a made electrode..and a #4 AWG GEC to cold water..correct?

thanks

mustang

thanks for any replies.
_________________________
Electricity has no respect for ignorance!

Top
2014 / 2011 NEC & Related Books and Study Guides
#89654 - 10/12/04 03:05 PM Re: Building Steel GEC or Water Pipe GEC?
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
You must use all available electrodes. See 250.50

As far as the sizing goes, yes, you are correct.
_________________________
Ryan Jackson,
Salt Lake City

Top
#89655 - 10/12/04 03:07 PM Re: Building Steel GEC or Water Pipe GEC?
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
250-50 says if available bond every thing together. sizes look good. #4 also to the steel.
Ryan you beat me

[This message has been edited by trekkie76 (edited 10-12-2004).]

Top
#89656 - 10/12/04 04:22 PM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
so you are saying that there SHOULD be a cold water bond IF AVAILABLE?

i am asking because i am working from a set of plans that just ask to bond to three 3/4 X 8' ground rods and to the building steel. the building has copper piping installed. i always bond the copper at the point of entry into the building or first accessible loc

should i make a revision on the dwgs and call for a COLD WATER BOND using a #4 AWG? and should I revise the dwgs to call for a #4 AWG to the ground rods and the building steel? I though #6 was good for MADE ELECTRODES?

sorry if this is elementary to you...grounding is the most important part of any electrical system and it is one of the FUZZIEST too!

i am big on grounding!

thanks

mustang
_________________________
Electricity has no respect for ignorance!

Top
#89657 - 10/12/04 04:35 PM Re: Building Steel GEC or Water Pipe GEC?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
This may help



The engineer is free to ask for more than code minimums.

The Power company around here asks for 4/0 to 3/4" 10' ground rods at transformer pads.

The NEC would say 6 AWG would be enough.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#89658 - 10/12/04 04:36 PM Re: Building Steel GEC or Water Pipe GEC?
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
Yes, if it is there and meets the description of an electrode, you must bond it with (in your case) a #4.
_________________________
Ryan Jackson,
Salt Lake City

Top
#89659 - 10/12/04 05:46 PM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
yes that slide clearly shows the best means to accomplish a proper grounding system

That looks like the same slide on the first page of the NEC handbook

and thanks for the follow up comments regarding the #4

thank you very much!

mustang



[This message has been edited by mustangelectric (edited 10-13-2004).]
_________________________
Electricity has no respect for ignorance!

Top
#89660 - 10/13/04 07:33 AM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member

Registered: 02/08/04
Posts: 496
Loc: Bentonville, AR
are the articles:

GEC:250.66
Bonding Jumper: 250.122

regards

mustang

[This message has been edited by mustangelectric (edited 10-13-2004).]
_________________________
Electricity has no respect for ignorance!

Top
#89661 - 10/13/04 07:51 AM Re: Building Steel GEC or Water Pipe GEC?
eprice Offline
Member

Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
 Quote:
are the articles:
GEC:250.66
Bonding Jumper: 250.122


No, when we're talking about bonding jumpers within the grounding electrode system, they are also sized according to 250.66. (see 250.53(C))

Top
#89662 - 10/13/04 02:29 PM Re: Building Steel GEC or Water Pipe GEC?
trekkie76 Offline
Member

Registered: 06/19/04
Posts: 219
Loc: baileyville, maine, usa
to the made electrodes does only have to be #6. I was talking about to the steel being #4

Top