#89653 - 10/12/04 02:20 PM Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
Hi,
Is connecting the gec to building steel on a commercial job accpetable versus cold water bond?

it seems to me that you need both but parallel paths could be an issue.

i am looking at a riser diagram that calls for 3 3/4"X8' ground rods placed 10 feet apart and instructions to connect to building steel where possible..

it seems to me that you need a building steel connection and you need a cold water bond..200A service requires a #6 AWG GEC to a made electrode..and a #4 AWG GEC to cold water..correct?

thanks

mustang

thanks for any replies.
_________________________
Electricity has no respect for ignorance!
Top
2017 / 2014 NEC & Related Books and Study Guides
#89654 - 10/12/04 03:05 PM Re: Building Steel GEC or Water Pipe GEC?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
You must use all available electrodes. See 250.50

As far as the sizing goes, yes, you are correct.
_________________________
Ryan Jackson,
Salt Lake City
Top
#89655 - 10/12/04 03:07 PM Re: Building Steel GEC or Water Pipe GEC?
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
250-50 says if available bond every thing together. sizes look good. #4 also to the steel.
Ryan you beat me

[This message has been edited by trekkie76 (edited 10-12-2004).]
Top
#89656 - 10/12/04 04:22 PM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
so you are saying that there SHOULD be a cold water bond IF AVAILABLE?

i am asking because i am working from a set of plans that just ask to bond to three 3/4 X 8' ground rods and to the building steel. the building has copper piping installed. i always bond the copper at the point of entry into the building or first accessible loc

should i make a revision on the dwgs and call for a COLD WATER BOND using a #4 AWG? and should I revise the dwgs to call for a #4 AWG to the ground rods and the building steel? I though #6 was good for MADE ELECTRODES?

sorry if this is elementary to you...grounding is the most important part of any electrical system and it is one of the FUZZIEST too!

i am big on grounding!

thanks

mustang
_________________________
Electricity has no respect for ignorance!
Top
#89657 - 10/12/04 04:35 PM Re: Building Steel GEC or Water Pipe GEC?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
This may help



The engineer is free to ask for more than code minimums.

The Power company around here asks for 4/0 to 3/4" 10' ground rods at transformer pads.

The NEC would say 6 AWG would be enough.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#89658 - 10/12/04 04:36 PM Re: Building Steel GEC or Water Pipe GEC?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Yes, if it is there and meets the description of an electrode, you must bond it with (in your case) a #4.
_________________________
Ryan Jackson,
Salt Lake City
Top
#89659 - 10/12/04 05:46 PM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
yes that slide clearly shows the best means to accomplish a proper grounding system

That looks like the same slide on the first page of the NEC handbook

and thanks for the follow up comments regarding the #4

thank you very much!

mustang



[This message has been edited by mustangelectric (edited 10-13-2004).]
_________________________
Electricity has no respect for ignorance!
Top
#89660 - 10/13/04 07:33 AM Re: Building Steel GEC or Water Pipe GEC?
mustangelectric Offline
Member
Registered: 02/08/04
Posts: 494
Loc: Bentonville, AR
are the articles:

GEC:250.66
Bonding Jumper: 250.122

regards

mustang

[This message has been edited by mustangelectric (edited 10-13-2004).]
_________________________
Electricity has no respect for ignorance!
Top
#89661 - 10/13/04 07:51 AM Re: Building Steel GEC or Water Pipe GEC?
eprice Offline
Member
Registered: 08/07/03
Posts: 64
Loc: North Logan, Utah, USA
Quote:
are the articles:
GEC:250.66
Bonding Jumper: 250.122


No, when we're talking about bonding jumpers within the grounding electrode system, they are also sized according to 250.66. (see 250.53(C))
Top
#89662 - 10/13/04 02:29 PM Re: Building Steel GEC or Water Pipe GEC?
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
to the made electrodes does only have to be #6. I was talking about to the steel being #4
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals